I did give you one. You can't put arc fault breakers on a shared neutral.
It may not apply to your situation. But, it is a legitimate reason.
I have no plans of using AF breakers. Just standard breakers
I'll test it with an ammeter this weekend and post an actual picture of the read-out with two identical fans on the same speed setting, sharing a neutral on opposite poles of the center tap.
Looking forward to the test.
I (and I dont think anyone else) is saying that there will never be amperage on the neutral. Just saying that it will never see more than 20A.
I assume this is how you are going to conduct your test:
Simple 2 hots and a N going out to two receps. First recep gets line 1, second recep gets line 2. Both use the same neutral
It is unlikely that you will find two things or fans that will pull an identical load. So lets say you load line 1 up with 5A and load line 2 up with 6A. The neutral wire BETWEEN the outlets will read 6A
The neutral wire between the box and the first outlet will read 1A. Because the 5A from outlet 1 is SUBTRACTED from the 6A from outlet since the hots are on different phases.
I think you are assuming they get added together. But that would only be the case if the two hots were on the same phase in the panel.
The MOST current the neutral will have in a proper shared circuit is 20A. And that is if one of the circuits is pulling a full 20A, and the other 0A. Add current to the second and it starts to subtract off the 20A.
Look at the feed coming into your main breaker box. Two 120v legs capable of 200A each. With a single shared neutral for return. (which is allowed to be downsized a bit) cause the only way it would ever see 200a is if you were pulling a full 200A on one leg, and 0A on the other. Which is very unlikely to ever happen.