farmer2009
Elite Member
When turning things off remember that each leg alernates sides in the panel. It doesn't run straight down one side. This is how a double breaker gives 240.
I agree with this comment.I am also electric lineman.Make sure to check all of your grounds in your fuse panel to make sure they are tight also.With the main breaker OFF.Not all lineman trouble shooters are created equal,some are better than others.When I was a troubleshooter (lineman) for the utility company we always put load on the "high side) of the (one phase at a time)customers meter cabinet. If the other phase spiked while the one we tested dropped, it was obviously a open nuetral. Their could be several reasons for that, bad URD cable, connection at pedestal or transformer, etc. If we saw no drop in voltage between phases it was usually on the customers side. Their was of course, some other more complicated rare examples that required more troubleshooting.
You need to put load on (microwave) each phase and test. Keep backing up from the main, to the meter, to the ped, risor pole, etc until you get balanced load, then You'll find your problem
When turning things off remember that each leg alernates sides in the panel. It doesn't run straight down one side. This is how a double breaker gives 240.
I think I follow you but in layman's terms do you think the most likely source of the faulty neutral is in my buried cable?More like : ///////resistance/////////120V (Line-Neutral)) (L1) ----- // | // | // | /////////// Nuetral/////Zero 0-Volts//////(Grounded/Earth) 240V (Line to Line) // | // | // | ///////////resistance)////////120V (L-N)(L2) __|___ but then neutral connection, or it's bond with ground/earth goes bad, and the neutral is not pegged to O volts, thus the 240V L-L is not evenly divided in half to 2 phases of 120V (L-N), instead, now the 240V (L-L) is split across the two resistances, in proportion to one (L1) circuits resistance compared to the others (L2) circuits resistance. (Example if L1 resistance is twice the size of L2's, then the voltage will split 1/3 (60volts) in 1 circuit and 2/3 (180V) in the other.) The way the 240V L-L is split and the voltages measured in any one circuit will change as you switch different resistences (loads) in and out of the circuit, but always add to 240V. With a floating neutral , it now looks like this: ///////resistance (twice that of ckt. L2)/////////160V (Line-Neutral)) (L1) ----- // | // | // | /////////// Nuetral///// -- Not connected to (Grounded/Earth, O Volts) 240V (Line to Line) // | // | // | ///////////resistance)////////80V (L-N)(L2) ----- Edit: Grrrr. My vertical lines showing constant 240V between ckt L1 and L2 don't align.