Lesson learned on Romex and conduit. LOL, as others, abandon and do it right.
Ron
Ron
Lesson learned on Romex and conduit. LOL, as others, abandon and do it right.
Ron
Make the repair where it broke and forget about pulling a section out, it's not going to work. Install a waterproof J-box, splice a new section of wire to the two broken ends and seal it up. Put a new section(s) of conduit to existing by using couplings and glue, run the lengths of new conduit into the j-box and seal them into box. Mark location so you can go back later if need be. Done.
Next time run single stranded wires through the conduit instead of Romex, and use a pull cord so to be able to fix things like your current problem more easily. Current problem, get it, current problem!:laughing:![]()
Is this standard white jacket Romex with a paper sheath, like you'd run in the walls of a home? If so, it's probably going to fail at some point since it has very poor moisture resistance. This might be a good time to replace it all together.
It is a code violation to pull romex (NM-B) in conduit outdoors. The romex is not rated for damp or wet locations even if in a raceway (conduit). UF cable is required and can be direct buried without conduit until it comes out of the ground. 1/2" conduit is suitable for 3 conductors, black, white and green. Remember that the green wire is the most important wire in the group!