Power Line to my house was broken

   / Power Line to my house was broken #221  
Currently my red clay soil is very moist, so I have a really good ground. By summer, my soil will dry out and it wont be as good. I have a hot wire around my pasture that I had to put in three ground rods, ten feet apart, to get to work in the summer.

Every power pole has a copper wire running down the length of the pole into the ground. I'm not sure how deep they go, but there isn't a grown rod, just the bare wire stapled to the post.

Seems to me that I put in a ground rod when putting the meter base together, but it's not a good memory, so I'm not positive if there is one there or not. I have one ten foot ground rod at both of my panels at my house.

Is there a contact in TX to call and complain about this?
The ground wire generally goes to the bottom of the pole, and has a few wraps around the pole before the pole goes into the hole.

Is your wire still down?
 
   / Power Line to my house was broken #222  
The ground wire generally goes to the bottom of the pole, and has a few wraps around the pole before the pole goes into the hole.

Is your wire still down?
That is NOT correct information.The ground wire is usually #6 copper wire which is stapled to the pole(NOT WRAPPED) fed to driven ground rods a few feet from the pole..
 
   / Power Line to my house was broken #223  
That is NOT correct information.The ground wire is usually #6 copper wire which is stapled to the pole(NOT WRAPPED) fed to driven ground rods a few feet from the pole..
I am talking about it being wrapped down at the base, below grade. It was old practice here, usually called a butt-ground. Some utilities used plates, as well. Driven grounds would be spaced out along the line, or where there may be transformer or other equipment. Depends on the soil conditions.
 
   / Power Line to my house was broken #224  
I am talking about it being wrapped down at the base, below grade. It was old practice here, usually called a butt-ground. Some utilities used plates, as well. Driven grounds would be spaced out along the line, or where there may be transformer or other equipment. Depends on the soil conditions.
Worked in Texas doing storm work NEVER seen what you are speaking of.
 
   / Power Line to my house was broken #225  
As far as I know every utility pole that has a transformer on it in this area has a copper wire runing down from the outer casing of the transformer to the base of the pole and then has a coil of the wire stapled to the bottom of the pole.
 
   / Power Line to my house was broken #226  
I am talking about it being wrapped down at the base, below grade. It was old practice here, usually called a butt-ground. Some utilities used plates, as well. Driven grounds would be spaced out along the line, or where there may be transformer or other equipment. Depends on the soil conditions.
Not sure where "here" is for you....

But "here" for me in central ohio....this is very common
 
   / Power Line to my house was broken #227  
Friend of mine had phone lines hanging down off a polealong his road. He called and said there’s a crazy guy in the neighborhood who is going to cut it to pieces. He said they fixed it the next day.
 
   / Power Line to my house was broken #229  
Every pole I have ever set we have put a butt ground on it (being #6 copper pulled from the bud to the butt with about a 6' wrap stapled to the butt of the pole , if we are hanging a pot or lightning arrestors, cap bank etc we will also drive rods in addition to the butt ground, this is a very common practice in the South.
 
   / Power Line to my house was broken #230  
Worked in Texas doing storm work NEVER seen what you are speaking of.
it is a common practice here Coobie. Every pole, before it is set has a spiral wrap on the bottom of the pole with the #6 wire. Of course it is stapled all the way down the pole and then the spiral wrap on the bottom of the pole.
 
   / Power Line to my house was broken #231  
Googled (actually used Bing) "telephone pole butt ground" and went to images.....
DDE7F4A1-03D4-47C5-9DF1-491E6813FA1D.jpeg
 
   / Power Line to my house was broken #232  
it is a common practice here Coobie. Every pole, before it is set has a spiral wrap on the bottom of the pole with the #6 wire. Of course it is stapled all the way down the pole and then the spiral wrap on the bottom of the pole.
I thought I had mentioned this up thread but maybe I only thunk it. :unsure: :D

Years ago they were replace power poles in town, and before they put the poles in the ground, the poles were just laid out along the side of the road. I noticed that all of the poles had a copper wire running down the pole and at the bottom of the pole the wire was in a nice, neat coil. The coil and wire were stabled to the pole.

This was when copper theft was a big problem and I thought they were taking a chance leaving the poles out with that tempting copper just sitting there. Best I could tell, none was stolen. (y)

We have had so much growth, the "new" poles are being now replaced with bigger and taller poles. :eek:

Later,
Dan
 
   / Power Line to my house was broken #233  
Great thread with lots of useful information.
 
   / Power Line to my house was broken #235  
Never seen that before here in the north country ..
Me, either, but I wonder if it has a lot to do with the soil depth that you can expect a reasonable ground at. Soil that is too dry / too sandy / too rocky isn't going to function well.

Or do you think it has to do with grounding lightning strikes better?

Either way, this has been a really interesting thread. Thanks to everyone for contributing. Personally, I find it hard to believe that @EddieWalker is still partially wired...

All the best,

Peter
 
   / Power Line to my house was broken
  • Thread Starter
#236  
Still not fixed. I'm hoping that with the rain coming fairly steady, the ground will remain wet and I'll continue to have a good ground until the fix it.

I've been wracking my brain to try and remember how they did the ground wire on the poles when they installed them. I remember seeing a guy unroll the copper and staple it to the pole when it was still laying on the ground, but I don't remember what he did with it at the bottom of the pole.
 
   / Power Line to my house was broken #237  
Unreal. Just unreal.

I hope that you stay safe. With the rain, I certainly expect your home grounds to be going to stay in good shape.

All the best,

Peter
 
   / Power Line to my house was broken #238  
A related update:
In the process of adding battery backup to the house. It is a process. In our case, a very long drawn out process because the battery supplier hasn't supplied very many batteries last year or this year. As in we ordered the batteries spring 2020.

Well good things come to those who wait, or so I have been told. Batteries finally arrive at the electricians.

First the main panel has to be replaced with one that has upgraded 225A busbars. Get the power company out to cut the overhead wires. Literally. The lineman crawls on the roof and cuts the cables, wraps them in electrical tape and leaves. Cut the old panel out of the side of the house, pull the old service drop (4/0Al!), install new service drop (copper), install new panel, reinstall existing circuits. Wait for the lineman to come back. He does, and splices the old overhead wires into the new service drop and leaves. House back on six hours later. Everything works.

Then install the batteries, automatic transfer switch for the batteries, move the solar connections to the automatic transfer switch, add a panel to take all of the circuits to be backed up by the batteries, all without turning off the house power. Three days, lots and lots of wiring, and large conduits.

Now comes the fun bit; you have to turn off the house power to move the house circuits out of the new (3 day old) panel, into a newly installed backup panel, and install a 200A breaker in the main service panel to feed the automatic transfer switch and backup panel. Following this? Yes, the wiring gets convoluted, but all according to NEC rules.

After moving the wires, turn the main service disconnect on.

Nothing happens. No power. The smart meter is blank. I figure that a fuse blew on the power pole.

Ok, I will call the power company, but first I get out the extension cords generator and get the essentials on power. While doing that I notice a surge strip with a green LED on. WTH? I go back to the main panel, and measure 16V on one phase. Throw the service disconnect off. The smart meter now comes on as far as reading out idiot lights "88888". Ok, call the power company, figuring the fuse blew on the power pole.

The lineman turns up promptly, he is the same guy who spliced in the new service drop on day one, so he knows what is going on. After poking around, he heads out to check main line fuses farther away, as those have easy access. Ninety minutes later, he comes back; "you need to have your transformers replaced. The crew will be out later tonight, or tomorrow morning." :(

Not too surprisingly, the crew comes out the next morning, and proceed to drive two large bucket trucks up and across slopes that my slope tractor has challenges with. Thirty degree slopes. They can't get their biggest truck up there, so they have to rig a pulley and winch to lower the old transformers off, and the new ones up. After a couple of hours and quite a bit of work for everyone on the six man crew, it is done. They mention in passing that they had to replace the ground wire for the pole. I am not surprised.(More on that in a moment.) Two years ago, the power company contractors worked on the pole adding rot preventative, and checking the ground, which I happened to see. So I know it was good then.

Moving on. Now, we get to experience the bad news. Flipping the service disconnect works, but then flipping on the main breaker that feeds everything fails. As in "BANG", with lots loud humming and arcing noises, fails.

As all of this happened while the panels were being rewired, the suspicion is on the rewiring, although it is hard to see how. Time to get the rewiring crew back out.

They pull the panels, and start tracing the wiring. Long, long story short, it turns out that there are two tiny teeth (less than 1/8") on the underside of a terminal for a 4/0 main busbar terminal for the neutral wire from the main panel to the automatic transfer switch. One of the two teeth is bent/missing, which has the effect of not completing the neutral circuit, resulting in a floating ground, blowing the breaker.

Whether the increased neutral flow pushed the transformers over the edge, I don't know.

Here is why I wasn't surprised to have a melted ground wire on our transformers: We had a doozy of a lightning storm a year ago, the one that started last summer's fires here in California. Eleven thousand lightning strikes or so. Since then, the power company has been replacing transformers along miles of power lines toward our place. They were due to replace ours the day before this happened, but they canceled at the last minute, so I suspect that they knew the transformers were dying.

Which leads me to wonder if @EddieWalker has had his grounds/power lines repaired.

Stay safe out there.

All the best,

Peter
 
   / Power Line to my house was broken
  • Thread Starter
#239  
The short answer is no. Nothing has been done. I looked back to when I started this thread and it was in March. Nothing has happened at the Gas Pipeline Station, where they broke the wire, for months now. I really need to find a good phone number to call somebody that will actually do something. Thanks for the reminder, and for sharing your story.
 
   / Power Line to my house was broken #240  
Im not sure if texas has a public utilities commission. The puc can issue fines to companies that dont repair work. i had to file on a ziply phone line that i waited on for 2 months for them to pull old pole out and cut dead feed wires. I was warned that if i do it there is up to $10,000 fines. They said they would do it but never showed up. We filed a report and they were out next day to do removal.
 

Marketplace Items

2018 CATERPILLAR 259D SKID STEER (A60429)
2018 CATERPILLAR...
1987 CATERPILLAR D6H HIGH TRACK CRAWLER DOZER (A52709)
1987 CATERPILLAR...
Crown RM6025-45 Stand-On Electric Forklift (A59228)
Crown RM6025-45...
Honda EM3800SX Portable Gasoline Generator (A59228)
Honda EM3800SX...
2021 CATERPILLAR 299D3 SKID STEER (A60429)
2021 CATERPILLAR...
2016 Ford Transit 350 Cargo Van (A59230)
2016 Ford Transit...
 
Top