I agree with Rob that you will need an expert to blame if it doesnt work. The trouble is that unless you have a real expert they arent going to want to do a minimalist system - they will want to go ample. With bigger performance margin they are more sure you wont have any complaint. Essentially you will be pushing anyone you hire toward a close accomodation of only the loads you have. You may have to study up in order to be able interact with them, or to make your own choices appropriately.I am assuming the elevator has an unloader valve to operate at start-up. The circ pump runs constantly, the only other surge would be the boiler burner draft fan, minimal in my guess. While I personally do not have the equipment to measure surge current, I am going by what demand(surge) I am billed for, so far a max of 21kW. Whille the measured demand has been as low as 14kW, I am also assuming the elevator start up would draw less than 14kW. So, I am hoping that a 22-25kW generator will suffice. Your expert advice is greatly appreciated. Thank you...
Rules of Thumb:
Most generators are capable of delivering 300% of the rated current for 10 seconds
... some generators are "prime-power rated" -- which is the continuous (24/7/365) power output that will result in reaching a specified lifespan (e.g. 10K hours before rebuild). Wrooster
I agree with Rob that you will need an expert to blame if it doesnt work... I doubt that it does, but IF that number truly captures the quick surges then you are good to go with a 21KW gen. Please check what demand really means. Ask more than one person and resolve any conflicting answers.larry
Yes, but with ALL that said, I have never seen or heard of a gen that will support 3x its rating for an instant, much less 10 sec. It has nothing to do with the engine driving it. Its that the gen saturates magnetically pretty near 1x. Above this point V output drops instantly. You get no more regardless how hard you drive it. Im sure there are deluxe gens that go higher than ~1.1x, but costly and far short of 2x.This is way too broad of a statement to support. It is dependent on the type of engine in use, the power generation method (direct-coupled alternator versus inverter), and about 87 other factors. For example, some generators are "prime-power rated" -- which is the continuous (24/7/365) power output that will result in reaching a specified lifespan (e.g. 10K hours before rebuild). Above the prime power rating, there is typically about 20% headroom on top of that specified for non-continuous power (say, an hour or so). And, of course there is also some peak/overload capability power which is generally more a result of the alternator rotor and engine flywheel inertia than anything else. An inverter type generator, for example, lacks this sort of mechanical inertia and therefore generally is a bad choice for motor starting applications unless special methods are employed.
That said, typical motor start inrush does not last 10 seconds; ~1 second is more like it. That's 60 rotations of a 2 pole alternator driven by a 3600RPM engine, or 30 rotations of a 4 pole alternator head driven by a 1800RPM engine.
Wrooster
Howdy,Yes, but with ALL that said, I have never seen or heard of a gen that will support 3x its rating for an instant, much less 10 sec. It has nothing to do with the engine driving it. Its that the gen saturates magnetically pretty near 1x. Above this point V output drops instantly. You get no more regardless how hard you drive it. Im sure there are deluxe gens that go higher than ~1.1x, but costly and far short of 2x.
larry
Howdy,
Alot really depends on how the genset itself is built. (inside components) My Tiger Power 30KW pto generator has a 90,000 watt surge capacity.
Are there any concerns with wet-stacking?
If the tractor is singing along at ~2550 rpm to maintain 540rpm at the PTO to maintain 60hz...this would be a BAD situation on a standalone diesel genset unless the generator is loaded at least 40% of capacity.
Is this "problem" non-existent on the tractor?
ac
This is way too broad of a statement to support. It is dependent on the type of engine in use, the power generation method (direct-coupled alternator versus inverter), and about 87 other factors. For example, some generators are "prime-power rated" -- which is the continuous (24/7/365) power output that will result in reaching a specified lifespan (e.g. 10K hours before rebuild). Above the prime power rating, there is typically about 20% headroom on top of that specified for non-continuous power (say, an hour or so). And, of course there is also some peak/overload capability power which is generally more a result of the alternator rotor and engine flywheel inertia than anything else. An inverter type generator, for example, lacks this sort of mechanical inertia and therefore generally is a bad choice for motor starting applications unless special methods are employed.
That said, typical motor start inrush does not last 10 seconds; ~1 second is more like it. That's 60 rotations of a 2 pole alternator driven by a 3600RPM engine, or 30 rotations of a 4 pole alternator head driven by a 1800RPM engine.
Wrooster
Fred,
I won't give you that answer and here's why:
First, you should pay an engineer to do a work sheet for you. ... You want someone to be responsible for their calculations and I would say PM me and I'll give you an invoice..."<end quote>
OK, thanks Rob. My reason for asking was to get some free advice, without any professional liability. Most engineers overdesign at the expense of their clients to cover their own Errors and Omissions. I'm a risk taker, and I accept that. The generator salesman wants to sell me a unit three times bigger than I need. The fuel salesman the same. I'm a survivor, just trying to get by. When the goin gets tough, every ounce of fuel really counts. That's why I originally posted your quote. We live in a wasteful society and we don't even know it, until we run out what we need. Just like our country has run out of affordable health care, because doctors order a lot of unnecessary proceedures to cover their own liability, and guess who pays. So, back to the drawing board I go...(BTW, what would you charge me to design the smallest, minimalist, survivalist back-up system that only gets used a few days a year, with a discount for waived professional liability?)
Fred, thank you for asking but I'm semi-retired now, most of my work is in electronic engineering using embedded microcontrollers and several audio designs I promised an editor. Perhaps one of the people here who found my solution overly simplified might be inclined to address your issue but, again, a 25hp hydraulic elevator mandates a bonded legal responsibility in my view.
Thanks for the advice. I checked with the power company and "demand" does not measure peak surge, only the average of maximum usage in five minute increments. They recommended I measure with a pulse monitor; so I am still learning.
For less than $10 at Harbor Freight you can get one that does the same: Digital Clamp-On Multimeter (note that you can only go over one leg of the wire going to the pump. If you go over both legs it doesn't read anything).For less than $100 (on Amazon.com--more at your local big-box) you can get an "amp clamp" will answer this question definitively. Be sure to get one with an "inrush current" measuring feature that will detect and hold the peak draw from the motor.

Hmm, does it read amps per leg, or just combined amps?This digital monitor comes with 4 wrap around clamps 2 large and 2 small. I clamped one around each of the incoming load legs from the meter. The probes then plug into the back of a small transmitter that will send the signal a couple of hundred feet to the receiver. It gives a read out in real time and stores a 2 year log I believe. The whole shebang is battery powered.
For less than $10 at Harbor Freight you can get one that does the same: Digital Clamp-On Multimeter (note that you can only go over one leg of the wire going to the pump. If you go over both legs it doesn't read anything).
Aaron Z
That was my thought in buying it... I have a nicer Ideal meter (which has a temp probe), but I cant even get a add-on amp-clamp for that price...That's a hard price to beat for a clamp on meter, even if you get just to kick around!
Hmm, does it read amps per leg, or just combined amps?
Does it read voltage and/or Hz?
Thanks
Aaron Z