Is there any updates on this valve. I am wanting to use joystick for the FEL for the angle on the snowplow mounted on my FEL. On the wiring couldnt you use 2 switches for the 3 solenoids. If you installed switches for #2 and#3 and connected the wire that energizes these solenoids to solenoid #1, since #1 has to be energized(closed) for #2and #3 to work?
Bill
Not quite. If you simply ran a wire from #2 to #1 and #3 to #1, all 3 solenoids would be energized regardless of which switch you activated. You would need to either activate #1 through a relay, or isolate #2 from #3 by putting diodes in each of the wires to #1.
On edit: you could also do it without relays or diodes if you used DPST switches, using separate poles to emergize the two solenoids.