I am looking at putting a 10 to 12KW standby generator with an automatic transfer switch. Does the transfer switch have to be rated for the panel rating (200a) or the generator rating (50a) although realistically a 100a switch?
 
/ Transfer switch #2  
If you have 200a service you will need a 200a transfer switch for a whole house setup. You can go smaller if you plan on only supplying some circuits.
 
/ Transfer switch #3  
Most of the automatic transfer switches are whole house. You would need to size the switch to the panel. Manual switches tend to be smaller and you have to pick out your circuits with critical loads. The generator must be of sufficient size to carry the load.
 
/ Transfer switch #4  
The two Generacs I installed at work a few years back had an 8 or 10 slot breaker panel built into them. They were 50A switches for 10Kw LPG gensets.

The idea is to feed the switch from your main panel with a 50A breaker and move you essentials to breakers in the xfer switch itself (essentially a subpanel) - fridge, pump, lights, ac, etc. When the power goes out the xfer switch flips from house feed to generator automatically and then back after house power returns. I'd consider this safer than feeding a 200A switch into your 200A panel - safer for the genset that is. A 200A panel is going to require a far larger genset than 10-12kw to carry the load in that panel.
 

Marketplace Items

HYDRAULIC TILTING BUCKET FOR MINI EXCAVATOR (A58214)
HYDRAULIC TILTING...
2021 CATERPILLAR 262D3 SKID STEER (A62129)
2021 CATERPILLAR...
2006 CATERPILLAR D6N CRAWLER DOZER (A62129)
2006 CATERPILLAR...
2011 AUXILIARY POWER UNIT TRIPAC (A60736)
2011 AUXILIARY...
2001 CHEVROLET C8500 FLATBED TRUCK (A62130)
2001 CHEVROLET...
2014 Ford Explorer AWD SUV (A61569)
2014 Ford Explorer...
 
Top