Just got done doing some tests. With ambient temperature at 86 deg, static pressure on both HI and LO side was 90 psi.
Put the gauges on and started the tractor and let run with following results.
Time...........LO.......HI.......Comments
9:59AM......90.......90.......measured static, turned A/C & fan on max
10:00AM.....28.......300......clutch engaged, cold air at vents
10:05.........28.......310......clutch engaged, cold air at vents
10:10.........28.......320......water drip profusely from vent hoses
10:14.........27.......325......clutch disengaged, compressor stopped
10:16.........74.......125......no compressor op
10:18.........88.......110......no compressor op
10:20.........100.....100.......bumped clutch front with handle, no op
10:30.........104.....105.......pressures stable, still no compressor op
10:35.........104.....105.......zero volts at clutch, still no compressor op
Going out on a limb here, it looks like the problem is either in the wiring to compressor or cutout switches. Also, looks like too much refrigerant with HI pressure going to and settling around 325 deg. According to info found online HI pressure should be settling around 200 deg.
I'm totally new at this. Am I going down the correct path and making the right conclusions?