How To Plumb Well Water Lines for 2 Homes

   / How To Plumb Well Water Lines for 2 Homes #1  

Pettrix

Platinum Member
Joined
Jan 17, 2012
Messages
622
Location
High Desert Southwest
Building a guest house now and the well is about 100 feet from the house. I am planning to run a 100' underground main water line into the guest house and come up under the slab and have the pump controller in the garage. Years later I will build a main house but the question comes into play on how to get water into the main house?

If the well pump controller is inside the garage of the guest house. I can't just run a tee water line from the well area to the main home because the controller in the guest house garage would never know that a pressure drop occurred and so the well pump wouldn't turn on. Am I correct?

I would essentially have to run a line FROM the guest house garage to the main house and both house would run off the one controller in the guest house garage?

Confused. Not sure on how to set this up.
 
   / How To Plumb Well Water Lines for 2 Homes #2  
You got it. Controller in the guest house runs the pump, and supplies both buildings. Just size it big, and you're good to go.

Since you are doing a slab for the guest house, run that tee now. Stub it outside of the slab, at the very least.

Better yet, lay out where the main house will go and run that line all the way there now. Cap it, mark the end of it.

On the supply end, you may not want to connect it yet, but you can. If you don't, cap it to keep critters and crud out of it. Make sure you plumb in the fitting for it, whether you connect it or not. If it were me, I'd connect it now, but have a ball valve separating the guest house water from the main house water. You want to be able to shut off either one without shutting off the other one.
 
   / How To Plumb Well Water Lines for 2 Homes #3  
Here is a little drawing, you could add more valves for isolation where you want. Are you using a constant flow well pump?
 

Attachments

  • scan0001.pdf
    180.3 KB · Views: 210
   / How To Plumb Well Water Lines for 2 Homes #4  
Run the line to near the future house now and install a lawn hydrant on the end. That will show where the water line is and give you water near the job site.
 
   / How To Plumb Well Water Lines for 2 Homes
  • Thread Starter
#5  
OK, so I will run the main water line from the well to the guest house garage under the slab. Then have the plumber install a shutoff valve and a "T" at the junction and the water lines will reenter the garage slab and then one line exists up inside the home and the other continues under the slab and exists out the side of the guest house and terminates at a Frost Free.

When the Main House is built, I will just dig up the Frost Free and continue pulling the line to the Future Main House under ground and have it come back up inside the garage of the Main Future Home.

See my detail...

20160812_225007.jpeg
 
   / How To Plumb Well Water Lines for 2 Homes
  • Thread Starter
#6  
Now with such a long water line from the well to the guest house (100 feet) and then from the guest house to the future house (100 feet). So about 200 feet of water line.

What size water line should I run? I'm thinking 1.25 or 1.50 inch due to the run and due to serving 2 homes.
 
   / How To Plumb Well Water Lines for 2 Homes #7  
Now with such a long water line from the well to the guest house (100 feet) and then from the guest house to the future house (100 feet). So about 200 feet of water line.

What size water line should I run? I'm thinking 1.25 or 1.50 inch due to the run and due to serving 2 homes.

You can "t" off the line coming from the well at any point in the run, AS LONG AS THERE IS NO CHECKVALVE between the guest house and well. The check valve in the well will prevent back flow.

Static pressure in they system will be the same (assuming identical elevation) at every point in the system.

I was on a similar system, Pressure switch was at the well house at one residence, my house about 1,000 ft away and at the same elevation. I finally drilled my own well to get off the community one but did keep the inerconnect in case of need.
 
   / How To Plumb Well Water Lines for 2 Homes
  • Thread Starter
#8  
You can "t" off the line coming from the well at any point in the run, AS LONG AS THERE IS NO CHECKVALVE between the guest house and well. The check valve in the well will prevent back flow.

Static pressure in they system will be the same (assuming identical elevation) at every point in the system.

I was on a similar system, Pressure switch was at the well house at one residence, my house about 1,000 ft away and at the same elevation. I finally drilled my own well to get off the community one but did keep the inerconnect in case of need.

So you are saying I can "T" off near the well and run one line to the guest house and one to the future house and still just have the controller sit in the guest house?

If you turn on the water at the main house, how will the pump know that it needs to turn on?
 
   / How To Plumb Well Water Lines for 2 Homes #9  
The water will back flow from the quest pressure tank to the house. I have this set up and put a pressure tank at each location to satisfy the short term demand and it increases the overall storage ( pump start stop fewer times). The static pressure will balance across the system .
I ran a separate line between locations so I'd have the water softener at one location to serve both house and guest house ( shop in my case)
 
   / How To Plumb Well Water Lines for 2 Homes #10  
Are there two locations at the same elevation? My basement gauge and controller in house is 10 feet below my shop gauge and reads 5 psi more than shop. It is 15 psi per 33 feet of water altitude change due to static water pressure. The static pressure in pipes is like skin diving in lake, one atmosphere ( approx 15 psi) per 33 feet of depth.

I get maximum 60 psi in house while only 55 psi in shop. I first thought it was gauge error. Any body need a calibrated electronic readout pressure gauge? ☺
 
   / How To Plumb Well Water Lines for 2 Homes #11  
I handled a very long run from the well to my house by putting a pressure tank and the well pump controller in a small "well house" at the well.

There is a second pressure tank in the main house, with a check valve that prevents backflow.

There are also intermediate tap points that provide irrigation water before the run gets to the house, and the amount of irrigation water is much larger than the house consumption. This has worked for years with no problems.
 
   / How To Plumb Well Water Lines for 2 Homes
  • Thread Starter
#12  
The future main house will be a few feet higher in elevation (maybe 5 feet).
 
   / How To Plumb Well Water Lines for 2 Homes #13  
I wouldn't worry about a 5' elevation difference, but if it turns out to be a problem, you can always add a pressure booster.

There are a number of ways you can do this, but the thing to keep in mind is, you want ONE controller. You can have as many pressure tanks as you want (in theory) as long as the pump can handle all of them.

And think about maintenance and think about potential problems. You want to make sure you can isolate both buildings (that means valves) and you want to make sure a burst pipe in one place doesn't drain the whole system (that means check valves). You also don't want a flushed toilet in one house to mean a cold shower in the other.

Maintenance is the reason I don't like a pump house located near the well head. You'll have to run power there, and you'll have to do maintenance there. I'd rather have it in a comfortable basement with lots of room. But... it IS a very workable solution.


Another approach is to forget the pressure tank. Pump to a storage tank, and then have separate pressure boosters to supply each building. This isn't as common a setup, but it has a number of advantages. For one, much less load on the pump. It also eliminates any problem with elevation differences, and one building affecting the pressure in the other building.

These folks show a setup with a conventional pressure tank after the storage tank, which is one way to do it.

Water Storage Tank Systems | Texas Water Services and Well Drilling

Since you are in the high desert, the advantages of this should be obvious. In case of a power failure, you still have water to drink for a while.

Whatever you do, go bigger than you think you need. Pump and tank and pipe sizes. You will be glad you did.
 
   / How To Plumb Well Water Lines for 2 Homes #14  
So you are saying I can "T" off near the well and run one line to the guest house and one to the future house and still just have the controller sit in the guest house?

If you turn on the water at the main house, how will the pump know that it needs to turn on?

It's a closed hydraulic system, pressure is the same throughout (static), It may take a bit for the controller to see the pressure drop there when a tap it turned on but it would be inperceptable.
 
   / How To Plumb Well Water Lines for 2 Homes #15  
Are there two locations at the same elevation? My basement gauge and controller in house is 10 feet below my shop gauge and reads 5 psi more than shop. It is 15 psi per 33 feet of water altitude change due to static water pressure. The static pressure in pipes is like skin diving in lake, one atmosphere ( approx 15 psi) per 33 feet of depth.

I get maximum 60 psi in house while only 55 psi in shop. I first thought it was gauge error. Any body need a calibrated electronic readout pressure gauge? ☺

Yep, rule of thrum is .5 psi per foot elevation. Really .46 IIANM but close enough for practical purposes. One may have to live with a higher pressure at the low elevation to get acceptable pressure at the higher one.
 
   / How To Plumb Well Water Lines for 2 Homes #16  
I wouldn't worry about a 5' elevation difference, but if it turns out to be a problem, you can always add a pressure booster.

There are a number of ways you can do this, but the thing to keep in mind is, you want ONE controller. You can have as many pressure tanks as you want (in theory) as long as the pump can handle all of them.

And think about maintenance and think about potential problems. You want to make sure you can isolate both buildings (that means valves) and you want to make sure a burst pipe in one place doesn't drain the whole system (that means check valves). You also don't want a flushed toilet in one house to mean a cold shower in the other.

Maintenance is the reason I don't like a pump house located near the well head. You'll have to run power there, and you'll have to do maintenance there. I'd rather have it in a comfortable basement with lots of room. But... it IS a very workable solution.


Another approach is to forget the pressure tank. Pump to a storage tank, and then have separate pressure boosters to supply each building. This isn't as common a setup, but it has a number of advantages. For one, much less load on the pump. It also eliminates any problem with elevation differences, and one building affecting the pressure in the other building.

These folks show a setup with a conventional pressure tank after the storage tank, which is one way to do it.

Water Storage Tank Systems | Texas Water Services and Well Drilling

Since you are in the high desert, the advantages of this should be obvious. In case of a power failure, you still have water to drink for a while.

Whatever you do, go bigger than you think you need. Pump and tank and pipe sizes. You will be glad you did.

I'm with you on the pressure tank, conroller, etc not in a hole in the ground. Those are where all the maintenance (except the pump) takes palce. Why people htink they jus thave to have a well house is beyond me. My nieghbor had a new well drilled, put the tank/switch in a room in a shed nearby...then put money into insulating and heating hat room to keep things from feezing. He totally ignored the fact the old system ran just fine with the tank/switch in the house basement.
 
   / How To Plumb Well Water Lines for 2 Homes
  • Thread Starter
#17  
It's a closed hydraulic system, pressure is the same throughout (static), It may take a bit for the controller to see the pressure drop there when a tap it turned on but it would be inperceptable.

So I CAN run two separate lines from the well using a "T" valve to split them (one for the guest house and and one for the main house).

SEE ATTACHED DETAIL -

20160813_140809.jpeg

So being it's a closed hydraulic system, once I turn on the water in the future main house, the water will flow from the line from the well and then then the guest house line will begin to drain back and cause the controller in the guest house to sense the pressure loss and kick on the well pump.

Is that correct?

So there shouldn't be any problems or issues later if I do it with the above way, correct?
 
   / How To Plumb Well Water Lines for 2 Homes #18  
I live in Florida so freeze is not a problem. However, what we do have is four houses/buildings being fed from one well.

We have a 4" well with a submersible pump. In our case, since "basements" are not a common (or practical) thing in Florida, we have all the controls at the well. My house is 400 feet in one direction from the well and my Brother's house is 600 feet in the other direction - so, we have 1,000 feet of 1.5" mainline.

In your drawing it looks like you will have the controller in a free standing garage. Since the pressure switch sits on the mainline before it leaves the garage, and water drawn from it will be able to turn the pump on. If this is the case, feeding the other locations is simple, depending on how bad your areas freezes.

In the simplest way, just bring you mainline out and head toward the house(s). At some point, put a "T" and run one line to each house. Put a check valve where the water enters each house. Add an additional "T" in the mainline for any outside faucets/hydrants you would like.

If you don't have to great of a concern about in-ground freezing, you could place a "T" (or two) in the mainline just outside the garage and put a shutoff valve on individual lines running to each house and one for any outside watering. Put these valves in Irrigation Valve Boxes (the deep rectangular ones).

If ground freezing is a problem, you could always build a manifold in the garage (with cut-off's) and run each line out through the slab.

As long as the pressure switch is BEFORE the manifold or T's, the system will work fine regardless of where the water is used.

(think about it ... turning on the kitchen faucet downstairs or filling the tub upstairs makes no difference, the pump still works as it should. The same holds even if the kitchen faucet was in one house and the tub were in another)

BTW - we have had our system in and working for 40 years and we can never tell when water is being used in any of the other houses/buildings - and we only have one pressure tank ... it is at the well with the controller.
 
   / How To Plumb Well Water Lines for 2 Homes
  • Thread Starter
#19  
How big of a water line should I get from the well so I don't have volume/pressure losses?

1.25" or 1.50"
 
   / How To Plumb Well Water Lines for 2 Homes
  • Thread Starter
#20  
I'm confused now. Some are saying to run a single line from the guest house and then split it. Others are saying to run two main lines (one to each house) and just have the controller in the guest house garage.
 

Tractor & Equipment Auctions

HIGH END MINI GOLF CART (A58214)
HIGH END MINI GOLF...
SDLD25 MINI DUMPER (A58214)
SDLD25 MINI DUMPER...
UNUSED FUTURE FT-180H HYD ROTARY TILLER (A52706)
UNUSED FUTURE...
HIGH END MINI GOLF CART (A58214)
HIGH END MINI GOLF...
1459 (A57192)
1459 (A57192)
2001 Chevrolet Suburban SUV (A59231)
2001 Chevrolet...
 
Top