ponytug
Super Member
all propane installations use 2 regulators. a primary one at tank that allows for high pressure and another at generator that drops pressure to meet generator requirements. that unit needs a 2nd regulator that can provide up to 605,000BTU of fuel and the unit has to allow between 7-14" water column of pressure at start up and running. this level is not supposed to fluctuate more than 1" on the meter. do you know weather anyone actually used a manometer while starting and running?. if there is a surging issue i can almost guarantee its a fuel issue. personally i see so much wrong with that picture, its amazing. generac recommends at least 10 feet of 1-1/4" pipe between regulator and generator to allow for a storage area for fuel to assist with start up. second, i do not see any type of a drip leg to protect system from contamination. third, that looks like galvanized pipe which is not supposed to be used on gas systems (need black iron pipe. galv pipe can create flakes of galv coating entering system among other stuff), and the instructions clearly state to not bend the flex pipe, and to not attach flex pipe directly to the generator feed. you need to cross reference regulators to see if they can handle the huge load that unit puts on system.
Awesome!
So, I did check the regulator specifications, and the two regulators that have been installed can supply the 250cu.ft./hr / 605,000BTU/hr., if they are adjusted properly.
I will try to find out if the regulators were adjusted under load.
Thanks!
All the best,
Peter