Guys, here's a thread I started on fume extractors: https://www.tractorbynet.com/forums/welding/429959-dyi-fume-extractor-ideas.html
Actually, another thought here about gfci's...so I know they're code for 110v outlets in the garage. I don't think they're required for 220v though, kind of strange actually. Any of you have 220v gfci's?
Gfci is not required on 240v shop equipment. Only on 120v outlets.
2017 Code Language:
210.8(B) Other Than Dwelling Units. All single-phase receptacles rated 150 volts to ground or less, 50 amperes or less and three-phase receptacles rated 150 volts to ground or less, 100 amperes or less installed in the following locations shall have ground-fault circuit-interrupter protection for personnel.
ALL 120v outlets. Including refrig or freezer and garage door opener.Does that include a single dedicated outlet behind a garage freezer and a dedicated above 8' outlet for door opener?
All of my code books date from the 1980's when I was heavy into additions and remodels ..
Does that include a single dedicated outlet behind a garage freezer and a dedicated above 8' outlet for door opener?
All of my code books date from the 1980's when I was heavy into additions and remodels ..
im an electrical contractor. Different states use different parts of the NEC. Here in Idaho they never adopt the entire code. But an electric vehicle charger does NOT have to be gfci protected under current codes.A circuit that's dedicated to a machine -not a plug-in- doesn't require a GFCI, that is my reading (all code seems pretty clear on this). Doesn't matter what it is (welder or compressor).
A receptacle that is for an EV DOES require a GFCI protected circuit. The way I read this is that it's really the same for my situation, a plug-in (welder). The theory is the same.
Curious, are you an electrician? I'm intrigued by this issue and am thinking about asking my electrician: though, I actually taught him something that he wasn't all that up on (pertaining to wiring generators for dedicated power)![]()
A circuit that's dedicated to a machine -not a plug-in- doesn't require a GFCI, that is my reading (all code seems pretty clear on this). Doesn't matter what it is (welder or compressor).
A receptacle that is for an EV DOES require a GFCI protected circuit. The way I read this is that it's really the same for my situation, a plug-in (welder). The theory is the same.
Curious, are you an electrician? I'm intrigued by this issue and am thinking about asking my electrician: though, I actually taught him something that he wasn't all that up on (pertaining to wiring generators for dedicated power)![]()
Theres nothing wrong with having them GFCI protected, its just that i personally hate forcing someone to gfci their freezer, having the gfci fail , and lose $1,000 + Worth of food. Believe me ive seen this happen too many times to count. And come on, why does a garage door opener need to be gfci protected. Its nuts.
Gfci of 120 receptacles In garage or shop was required due to the fact that someone could plug an extension cord into outlet and run a saw, or some sort, outside. I can see that. But no one is going to plug into a 240 ev outlet and run a cord outside and run a saw. Thats why 240’s were exempt. Now they just want to regulate us to death. Just yesterday i got a call from an old client that their lake pump failed. No water in house. The GFCI breaker had failed. He went to home depot and lowes.....no one has any in stock. Just try to find a homeline gfci right now. He had to bypass gfci or not have water. Yet hes still alive. He ordered a new breaker on amazon.....well see.
And its just amazing that there are millions of older houses out there without a single GFCI or ark fault breaker and the occupants are still alive.
Theres nothing wrong with having them GFCI protected, its just that i personally hate forcing someone to gfci their freezer, having the gfci fail , and lose $1,000 + Worth of food. Believe me ive seen this happen too many times to count. And come on, why does a garage door opener need to be gfci protected. Its nuts.
Gfci of 120 receptacles In garage or shop was required due to the fact that someone could plug an extension cord into outlet and run a saw, or some sort, outside. I can see that. But no one is going to plug into a 240 ev outlet and run a cord outside and run a saw. Thats why 240’s were exempt. Now they just want to regulate us to death. Just yesterday i got a call from an old client that their lake pump failed. No water in house. The GFCI breaker had failed. He went to home depot and lowes.....no one has any in stock. Just try to find a homeline gfci right now. He had to bypass gfci or not have water. Yet hes still alive. He ordered a new breaker on amazon.....well see.
And its just amazing that there are millions of older houses out there without a single GFCI or ark fault breaker and the occupants are still alive.
As soon as you learn to appreciate EPA approved "SAFETY" gas cans,benifits and life enrichment afforded by GFI will become very clear.