Can someone explain this further, as I mentioned in the other E thread I have several shared neutral circuits but they are all on single breakers.
Can power go thru neutral some how from the live circuit, if you were working on a shut down circuit, if both were sharing the same neutral?
Is it code?
Thanks JB.
Hi JB,
Couldn't you ask an easier question? That's a good one. Part of the problem is, the NEC has been changing the requirements for multiwire circuits several times over the last few codes, so we're all a little confused.
Answer to one of your questions is yes. If you have a multiwire circuit and only shut of one of the two breakers, the neutral (white) wire that is shared can give you a nasty surprise! That's why multiwire circuits need to have provisions for simultaneously shutting off both hot wires.
The 2008 NEC is particularly vexing because it seems to contradict itself. I don't really want to get into that because we're trying to explain things here, not make them more difficult to understand.
The main point is to be able to simultaneously disconnect both hot wires of multiwire circuit.
The 2011 NEC does a better job. It wants the circuit to originate either at a double-pole breaker, or at two adjacent single-pole breakers with "identified" handle ties. (That means Square D handle ties for Square D breakers, GE handle ties for GE breakers, etc. No more using a bit of #10 copper, or a small nail as a handle tie!!)
One other requirement of multiwire branch circuits has to do with the neutral (white) wire. It is not allowed to rely on a device (such as a receptacle) for it's continuity. What that means is, while you may "feed in" and "feed out" the hot wires at the terminals on a receptacle, the neutral wires must be wirenutted together and a white pigtail used to connect the receptacle to the neutrals. A little hard to explain, so I hope this is clear enough.
Multiwire circuits have certain advantages, but with the requirements of Arc-fault breakers in houses now, if you're going to run a multiwire circuit you'd better make sure that you can get a double-pole AFCI for your panel. They are only available for a few makes of panels, and are rare as hens teeth. Note: you cannot handle-tie two single-pole AFCI breakers. It absolutely will not work.
I hope this was helpful in answering your question.
Mike