Burying a generator vault into a bank

   / Burying a generator vault into a bank #61  
That's unbelievable! What if the rope were to break or the wooden handle rots off? You'd be royally screwed! That's a technology trap if I ever heard of one!
 
   / Burying a generator vault into a bank #62  
That's unbelievable! What if the rope were to break or the wooden handle rots off? You'd be royally screwed! That's a technology trap if I ever heard of one!

I guess you would get another 50 cent length of rope and whittle a handle...

It was the standard for decades prior to recoil starters.
 
   / Burying a generator vault into a bank #63  
I guess you would get another 50 cent length of rope and whittle a handle...

It was the standard for decades prior to recoil starters.

First he'd have to walk the country roads looking for bottles to cash in for the deposit money to pay for the rope.... got any yucca plants? He could make his own rope. :)
 
   / Burying a generator vault into a bank #64  
I guess you would get another 50 cent length of rope and whittle a handle...

It was the standard for decades prior to recoil starters.

Yup. Am I the only one feeling incredibly OLD here??

Terry
 
   / Burying a generator vault into a bank #65  
I wonder if that applies to the Canadian Code.
It's common knowledge that free electrons in Canada act the same as all free electrons.
 
   / Burying a generator vault into a bank #66  
Haha I was thinking the same!

Also had a little crisis about the air compressor too. But the reality is I never use air tools. And the compressor runs a little while & shuts off (not like a generator). However if I HAD some tubing in my possession this morning, it would go in the trench!! Gonna cover it up by noon today. (snow tonite!!

What I have is Romex 10-2 & 12-2. My 12v pair is stranded THHN 10ga. For signal all I have is telephone cable 24ga. Why THHN ? (Thermoplastic High Heat Nylon). I'm doing my best to seal it but its like a level bucket. Seems like it could fill with water and remain full forever. I've been more worried about water than heat. (THWN Thermoplastic Heat Water resistant Nylon). Any ideas how to drain a level conduit with up-ends?


THHN will hold up to moisture quite well Romex will not. Next if you are running full power from the genset you should be using #8 or #6 sized wire. I would use #14 THHN for the low voltage wiring for the start/stop circuit. For the led lighting why not run it off the genset battery? If all else fails a good flashlight would be better for trouble shooting problems in the dark, you can aim it where needed.

If it were my project I would wait for the next trip and have the right materials on hand.
 
   / Burying a generator vault into a bank #67  
I run Air line everywhere. Makes for a nice reservoir of air. Recently I used 3/4 or 1" 200 PSI tubing, got off craigs list.

Do those BTU numbers account for much of the heat going out in the exhaust?

The exhaust gases are about half of the total heat loss calculation and are included. In this case the exhaust is not leaving the box on its own tailpipe.
 
   / Burying a generator vault into a bank
  • Thread Starter
#68  
THHN will hold up to moisture quite well Romex will not. Next if you are running full power from the genset you should be using #8 or #6 sized wire. I would use #14 THHN for the low voltage wiring for the start/stop circuit. For the led lighting why not run it off the genset battery? If all else fails a good flashlight would be better for trouble shooting problems in the dark, you can aim it where needed.

If it were my project I would wait for the next trip and have the right materials on hand.

I have a bank of 12v batteries in my shop. Prob better if the lighting is not related to the generator. Tomorrow it snows, and Turkey-day forecast is for 8 inches more. Today is the day to get this done or it's all winter with an extension cord under the snow, and the door held open by the cord. NOT this winter!

I think it will be fine - most folks just run the dang thing outside their shop door and listen to it. :D Neighbors too. :muttering:

489029d1479882236-burying-generator-vault-into-bank-img_7218-jpg


Gettin after it!

489030d1479882236-burying-generator-vault-into-bank-img_7219-jpg


OK to cover :D

489031d1479882236-burying-generator-vault-into-bank-img_7222-jpg


Like it never happened.

489032d1479882236-burying-generator-vault-into-bank-img_7223-jpg


Infrastructure! Now to figure out a door and add the ventilation.
 

Attachments

  • IMG_7218.jpg
    IMG_7218.jpg
    226.3 KB · Views: 252
  • IMG_7219.jpg
    IMG_7219.jpg
    245.2 KB · Views: 250
  • IMG_7222.jpg
    IMG_7222.jpg
    211.9 KB · Views: 259
  • IMG_7223.jpg
    IMG_7223.jpg
    148.9 KB · Views: 262
   / Burying a generator vault into a bank #69  
Looking good Sodo! :thumbsup: Looks like you have some block work in your future as well? Yep, I imagine your going to be covered with snow for awhile very soon! Good luck and keep us posted.
 
   / Burying a generator vault into a bank #70  
You should be able to pull new wire later through the conduit later when needed. Not hard to do with two 90 sweeps.
 
   / Burying a generator vault into a bank
  • Thread Starter
#71  
I read thru the thread again, Jenkins has taken the time to describe LOTS of good info on sound deadening and ventilation. Instead of rushing out to buy this $25 duct fan (6" & 435cfm) I probably should have bought the Harbor freight unit ($80/ 8" / 1500 cfm) per Curlydave. But he didn't post a pic so the info didn't go into the right memory slot.:rolleyes: Thats one of the problems of reading important info on a smartphone. I shoulda looked it up right away. Well anyway thanks Dave, and here's the link for posterity. :D Harbor Freight 8" 1500cfm ventilator fan $80

For 8,000 watts, (240vAC x 33A) 65 feet I get less than 2% voltage drop for 10ga wire. Seems sufficient because the times I'm truly working the generator full bore will be very seldom and short (couple second peaks?). In any case the wire is ready now, and as Jenkins noted it can be changed easily. Probably not by me though, I'll prob be all stinkbones before a deficiency shows up.

Dragoneggs its already snowing - not sure what to do with that dirt bank, might have to just let it find its own angle of repose (while I ought to do the same :D ) I can't though, too much other work to get done. Gotta weld today, and I'll be darned if I'm gonna uncoil my 50foot extension cord while theres a BEAUTIFUL buried conduit with everything I need.
 
   / Burying a generator vault into a bank #72  
I thought that was a 10,000 watt genset so yes you can get by with 10 gauge wire but it is maxed out.


The fan I posted was about $80 bucks but has a larger throat for better ventilation and comes with a built in temperature control to let it cycle automatically.
 
   / Burying a generator vault into a bank
  • Thread Starter
#73  
It's 8,000/10,000. My welder uses 7200 at max.

In general, I only need the 8,000w size for the inrush, and then welding is just a minute or two on, then off for awhile It doesn't labor all day at 8,000W. It's mostly just the engine running and needing to cool itself for all the noise it makes.

Well today I did a little testing. I directed to duct towards the "intake" end of the genset, that's all I could do with what I had (time & materials).

489148d1479965958-burying-generator-vault-into-bank-img_7231-jpg


With it closed up, (& 435CFM fan running as shown) the temperature quickly rose to beyond the range of the thermometer. The load on the generator is 160watts of lights, a 40A battery charger. So the generators barely working at all, just running it's engine.

489149d1479965958-burying-generator-vault-into-bank-img_7236-jpg


I ended up running it like this, with the plywood just to deflect noise. There's snow on the ground, this can't work in the summertime. Gonna need a lot more flow, I'm wondering if 1500CFM isn't enough. Maybe in the summertime it just can't be in the vault. I think I'm going to have to use one of my signal wires for a remote (temperature) alarm.
 

Attachments

  • IMG_7231.jpg
    IMG_7231.jpg
    176.5 KB · Views: 300
  • IMG_7236.jpg
    IMG_7236.jpg
    202.3 KB · Views: 247
   / Burying a generator vault into a bank #74  
Build a temporary wall 3' in front of the door and a couple feet wider so the sound coming out of the open door hits the wall and bounces up. See if that helps. Think an L shaped passageway like in front of a public restroom door.
 
   / Burying a generator vault into a bank #75  
I think you need to vent from the top or near and with a larger diameter fan maybe on a thermostat. I installed a 16in dia. louvered fan in my greenhouse and it really moves the air. It is fairly quiet with louvers. Something like this... Commercial Shutter Fan - Exhaust Fans | Greenhouse Megastore

Probably going to cost you about $200 with a controller/thermostat but you could mount to upper end of door with no ducting and allow for some draw at the bottom. Maybe the intake has a mesh vent to keep the hardy critters out. Forgive me... thinking out loud.
 
   / Burying a generator vault into a bank #76  
...I ended up running it like this, with the plywood just to deflect noise. There's snow on the ground, this can't work in the summertime. Gonna need a lot more flow, I'm wondering if 1500CFM isn't enough. Maybe in the summertime it just can't be in the vault. I think I'm going to have to use one of my signal wires for a remote (temperature) alarm.

In general, an internal combustion engine needs two sources of air, cooling air in and combustion air, and 2 more vents to remove air cooling air out and exhaust. In your situation you need only 3 since cooling air into the vault and combustion air in can be common. As you discovered, just pumping air into a closed chamber is not really going to cool anything since there really isn't any flow.

You need to both run your exhaust outdoors and allow a place for heated cooling air to leave. The air inlet can be constructed from plywood since it only handles ambient air. A square or rectangular cross-section plywood tube 4' long will do the trick here. Set it up with the ends closed and air inlets on the top or sides. Force the air flow to make 2 90 degree bends, which will allow the air to flow, but will attenuate the sound. If you got some of the sound deadening material used to line plenums in hot air heating systems to put inside the duct that would be the cat's meow. I would use galvanized heating duct for cooling air removal, since it is going to be hot. Again 2 90 degree turns, and here you really need the sound control since the duct is metal.

For the exhaust, I used steel exhaust pipe and a tractor muffler, but you could probably get by with gas vent pipe like one would use on a hot water tank. Although, routing the exhaust through a muffler does reduce sound levels.

The HF fan at 1500 cfm was low for my genset, which was larger than yours. You might get by with it, but if I were doing it again I would go larger.
 
   / Burying a generator vault into a bank #77  
I think you need to vent from the top or near and with a larger diameter fan maybe on a thermostat. I installed a 16in dia. louvered fan in my greenhouse and it really moves the air. It is fairly quiet with louvers. Something like this... Commercial Shutter Fan - Exhaust Fans | Greenhouse Megastore

Probably going to cost you about $200 with a controller/thermostat but you could mount to upper end of door with no ducting and allow for some draw at the bottom. Maybe the intake has a mesh vent to keep the hardy critters out. Forgive me... thinking out loud.
Skip the thermostat and have the fan turn on with the gen. :banghead: what was I thinking?
 
   / Burying a generator vault into a bank #78  
I've got both on mine.

A little ramp to go up over the intake duct would be a piece of cake.

Back in post #33 Jim offered an easy solution for moving the genset in and out over the raised floor.

My thought at the time was to mount the genset on a pallet frame of sorts to allow air beneath it. Your tractor could set it in the door easy.


What you lack is cross flow ventilation to eliminate hot pockets. Hot air naturally rises, so allow air in at the bottom and exhaust through the top. You need enough air volume in cfm to eliminate the temperature rise. The turns in the ducting help reduce the noise, but need to be lined with a sound deadening material. The ducting needs to be large enough to handle the job.

I would agree with Curly Dave that a muffler and exhaust would be best if the genset is stationary. About half of the overall heat is exhaust. A large muffler is fairly cheap. Using a muffler and a 1500 cfm fan/exhaust ventilator should fix you up.
 
   / Burying a generator vault into a bank #79  
All this compartment/enclosure discussion also makes me think about ventilation before you start the generator. All boats I know of use bilge blowers to remove fumes before starting the engines. Something you should think about before considering remote start options, you really need to open the door and vent that compartment well.
 
   / Burying a generator vault into a bank #80  
Not to needle you but it is easy to see how complex it can get trying to quiet the genset noise. My Honda inverter gensets operate near 58db or slightly higher, set around a corner of the hill these would be hardly noticed. My Onan diesel genset would be only slightly louder than the Honda. My Miller welder is just LOUD.
 

Tractor & Equipment Auctions

2023 MERCEDES BENZ SPRINTER 3500 CARGO VAN (A59905)
2023 MERCEDES BENZ...
2022 NEW HOLLAND 266BMM 66-INCH BELLY MOUNT FINISHING MOWER WITH SIDE DISCHARGE (A57024)
2022 NEW HOLLAND...
2020 FORD F-150 XL CREW CAB TRUCK (A59823)
2020 FORD F-150 XL...
2023 Kubota M4-061 Deluxe MFWD Utility Tractor with LA1154 Front Loader (A55315)
2023 Kubota M4-061...
Unused 2025 CFG Industrial H15R Mini Excavator (A59228)
Unused 2025 CFG...
2013 KOMATSU HM400-3 OFF ROAD DUMP TRUCK (A60429)
2013 KOMATSU...
 
Top