help! Stables construction - doorway header details

   / help! Stables construction - doorway header details #11  
what kind of trusses are you setting? if they are standard AG truss, 8' OC will have a 2x8 bottom chord or better. this means there is no "filler" required between webs if you stack other 2x8's behind it to beam the 10' opening.

But hears the deal, usually the gable ends are just regular full span trusses with addtional blocking. As such they are designed to carry a full 8' OC on full span.

but as your on a gable end, you only have to span 10', and if you have 0" overhang on the front you are only carrying 4' of load.

in other words, look at the weight of your door (a 2x4 wall with drywall both faces is usually speced out at 6psf,) so 10x13=130*6=780lbs for both doors /10'opening = 78plf on the bottom chord of the gable truss.

check with your truss guy but my guess is, your standard AG truss can support that weight already with no addtional header.

NOTE, the gable end truss is not designed to take horzontal windforce from the end of the building. You will have to make shure you properly brace the BC of the truss into the rest of the ceiling diaphram (which absorbs that horzontal force on the doors)


OTOH, if you are setting regular 2'OC 2x4 over2x4 trusses (common for a 30' wide building) you can have the truss plant insert a 2x8-2x10 on the bottom chord over the opening section to act as the above mentioned header when they build the gables. But thats if your gettting "custom" trusses and just not a spec 30' 4/12 1' OC fink truss.


(ps, i worked as an engineer for a ITW Alpine doing truss engineering for 5+ years, id pull up our softwere and run the truss myself to see if it would take the addtional load, but its late and im tired ;) )
 
   / help! Stables construction - doorway header details
  • Thread Starter
#12  
Thanks guys, consider the thread closed - I framed the doors conventionaly by setting 3 2x12 onto jack posts and running a 2x6 top plate for the end truss to sit on.
One thing that concerns me from what little research I've done and from schmism's comments is the horizontal wind load on the gable end truss - this seems to be a high point of failure in hurricane land. We get a fair amount of wind in our area so I will be looking to re-enforce the bottom cords.
 
   / help! Stables construction - doorway header details #13  
Mikes extra-thick/ double wall idea was a good one, should have thought of that myself

Even though gable end doesn't take roof load, you still want the "box" to be stiff for side loads. Earthquake loads add even more of course
 

Tractor & Equipment Auctions

2014 UTILITY DRY VAN TRAILER (A45677)
2014 UTILITY DRY...
2018 Dodge Charger Sedan (A46684)
2018 Dodge Charger...
2014 Therm Dynamics TD400 Towable Flameless Heater Trailer (A45336)
2014 Therm...
LGMG AS4046E 40 SCISSOR LIFT (A47001)
LGMG AS4046E 40...
2018 FORD F-550 ROUSTABOUT (A47001)
2018 FORD F-550...
2024 Big Bend 16FT x 6FT Bumper Pull Livestock Trailer - Durable Ranch-Ready Stock Hauler (A48561)
2024 Big Bend 16FT...
 
Top