PTO Generator

   / PTO Generator
  • Thread Starter
#21  
I don't know exactly what your draw is on that unit. I'm...pretty old - an AC compressor "bump" from start up might be 3X the running load in the past. Newer technology (aka "soft start") might not need that capability. Probably need to zero in on that math, though.

And, not at all trying to be flippant, but could not a fan(s) get you through an emergency? I have been out in cold temps for over a week, but I don't worry about air conditioning as much. Again, it's what you and your family will accept for a short time. And, frankly, a cheap window ac unit would cool you in one room in an emergency.

Just thoughts - what you want and do is up to you...
My in-laws were without power for over a week in the humid summer from a storm this year. It gets hot here and I don't like it, so I'd like to have the option.

As far as a window unit, we have casement windows that are horizontal in all of the bedrooms. It would have to be portable AC units. I figure if I'm going to spend money on it, I'd rather get more capacity than I need rather than less. I do agree that a winter extended power outage is more likely than a summer one. We had a bad storm last winter and power was only out for around six hours at the longest stretch.

I do need to do more load homework, but thought I would start here.
 
  • Good Post
Reactions: MMC
   / PTO Generator #22  
Actually, they make casement ac units, I have casement style windows in the back of my shop and a window unit in one of them as a supplement to the climate control in the shop itself.
 
   / PTO Generator #23  
Problem for me is uniform pto gen output. House has 240 V electric resistance baseboard heat, which cycles on and off per house thermostat guidance. Heat, not well, fridge, stove etc, is the largest load. When the demand on the generator changes the tractor throttle speed must be adjusted. There's no governor on tractor speed except the hand or foot throttle, which requires a manual visit to the tractor. Otherwise house voltage and/or frequency vary unacceptably. How do you guys with pto gens handle this ?
 
   / PTO Generator #24  
The "governor" is built into your tractors throttle control.
It should correspond to load changes and keep a steady engine rpm.
Is the whole house on one thermostat so it is a major load change to the generator.
How much does the power frequency drop when the heat cycles on.
Many pto generators have adjustable voltage regulators.
 
   / PTO Generator
  • Thread Starter
#25  
Problem for me is uniform pto gen output. House has 240 V electric resistance baseboard heat, which cycles on and off per house thermostat guidance. Heat, not well, fridge, stove etc, is the largest load. When the demand on the generator changes the tractor throttle speed must be adjusted. There's no governor on tractor speed except the hand or foot throttle, which requires a manual visit to the tractor. Otherwise house voltage and/or frequency vary unacceptably. How do you guys with pto gens handle this ?
In your case, I might consider shutting off the baseboard electric heat when running the PTO generator unless you have a very large one. My last place had baseboard electric and a 200amp panel to support it. If I were to run this on that house, I'd probably shut off all of the baseboard breakers and allow them to run one at a time. That place had a very effective wood stove in the basement and underground power, which I why I bought the small 240V generator so I could run the well.
 
   / PTO Generator #26  
Problem for me is uniform pto gen output. House has 240 V electric resistance baseboard heat, which cycles on and off per house thermostat guidance. Heat, not well, fridge, stove etc, is the largest load. When the demand on the generator changes the tractor throttle speed must be adjusted. There's no governor on tractor speed except the hand or foot throttle, which requires a manual visit to the tractor. Otherwise house voltage and/or frequency vary unacceptably. How do you guys with pto gens handle this ?
Are you sure your tractor does not have a governor? Most modern brands do. As long as it is working properly, a governor maintains RPM as the load varies. It does not increase or decrease it.

What tractor / PTO generator combination are you using?
 
   / PTO Generator #27  
My tractor is a 28 hp 1984 John Deere 950 and does not (so far as I know) have a governor. It also has an annoying "throttle creep" when working stationary. I override the creep with a velcro strap on the hand throttle. The generator is a Winpower 14 kW (now Winco ?) at least 10 years old. It does not seem to have any other regulation than PTO input speed. The generator body itself was made in France. Until recently I also regulated electrical consumption by switching on and off breakers to various loads. But this is getting tiresome, as is supplemental heating (after 15+ years) with a woodstove.
 
   / PTO Generator #28  
This is the parts diagram for the governor on the JD 950. You might check to see if they are all in place.

Here's the link to the Weingartz parts lookup page:


Unfortunately, most parts are no longer available.

Part of the problem might be the fact that the PTO on a 950 is rated at 27HP. Allowing for age and losses in the driveline, it may not be enough to allow your genny to produce full output. The rule of thumb is 2 HP per KW.
 
   / PTO Generator #29  
I've been looking at the Winco W15PTOS, it seems appropriate for what I need. I need to check the wiring on the transfer switch to make sure it can handle 60 amps.

I see they have some three point frames as well.
I just got this very setup. The 3 point frame comes with four rubber feet but is pre-drilled so you can replace the rubber feet with caster wheels which is very nice to roll it around the garage floor.

The bracket for the lower 3 pt pins is pretty weak and will bend as I found out.
 
   / PTO Generator #30  
Problem for me is uniform pto gen output. House has 240 V electric resistance baseboard heat, which cycles on and off per house thermostat guidance. Heat, not well, fridge, stove etc, is the largest load. When the demand on the generator changes the tractor throttle speed must be adjusted. There's no governor on tractor speed except the hand or foot throttle, which requires a manual visit to the tractor. Otherwise house voltage and/or frequency vary unacceptably. How do you guys with pto gens handle this ?

Any tractor with a pto has a governor.

If yours doesn't, get another tractor.
 
 

Tractor & Equipment Auctions

City of Tamp Odom reads 102152Year: 2014 Make: Dodge Model: Charger Vehicle Type: Passenger Car (A44572)
City of Tamp Odom...
2015 Ford F-550 4x4 Forestry Bucket Truck (A44571)
2015 Ford F-550...
Disc Attachment (A45336)
Disc Attachment...
2010 Crown Victoria Sedan (A44572)
2010 Crown...
2025 Ford E-450 Super Duty Incomplete Vehicle, VIN # 1FDXE4FN3SDD00021 (A44391)
2025 Ford E-450...
Continental BeltonTowable Sprayer (A45336)
Continental...
 
Top