Thanks for your vote of confidence. If you had read the first post, I said it was at least double.
According to Franklin, starting current can be as high as 6 times running current. Luckily, it's only for a moment. Once the motor gets started it should drop down to normal levels.
Also I took the time to list a chart which shows which gensets are recommend (by the manufacturer) to start/run a well pump.
According to Franklin, starting current can be as high as 6 times running current. Luckily, it's only for a moment. Once the motor gets started it should drop down to normal levels.
Also I took the time to list a chart which shows which gensets are recommend (by the manufacturer) to start/run a well pump.
The only thing I see that's wrong is in the first post of the thread.
Starting amperage is THREE times running amperage, not two times. That's standard acceptable practice according to the NEC.