Aaron, yeah I got the internet service set up early so I could get cameras going. It appears I have a couple overly nosey neighbors (and one that tried to cause trouble). I'm still working on getting the cameras set up, but am close.
   / A(nother) Home in the (different) Woods #162
What is it about neighbors. I thought I was moving to the middle of nowhere and ended up with the most miserable SOB's you could imagine. Did you mention the problems in this thread? Tell us more....I love hearing these stories.
   / A(nother) Home in the (different) Woods #163
Wisconsin requires a switch box if you feed a service from another building. Seems redundant to me, but OK. But then the inspector said I had to run the house as a subpanel from this, which I was very NOT OK with. This is a main service, and should be run as such. NEC says nothing about this that I could find, but I ran an extra ground to appease him. I think it is the wrong way to do it (and have questioned his judgement at many points), so I still think he is quite wrong, but I did it rather than fighting it. So here is the switch box for the house that sits on the shop. All utilities come to the shop first and are metered from there.
Ouch!!! Were you able to get the ground through the conduit ok?? I'm afraid the inspector is correct but only because of the stupid way that the code is written. If he had any common sense he should have allowed it. If the service came into the house first then you could have gone with your original plan but not the other way around because the garage isn't considered a "dwelling". Yeah, really stupid. :confused2:
If the code was written properly the easiest way is to install a 400 amp meter with double lugs on the load side and continue the 3-wire service to your house. But once a disconnect is installed then you have to go with a 4-wire subpanel. :mad:
edit: Oh.....also you can't have any other metal running between the buildings with a 3-wire service extension which is the only part that makes any sense to me.
I could not find that anywhere. Can you point me to a section? Given that it is fed directly from the meter, with nothing more than a simple disconnect, I don;t see how it could be required, but there are lots of silly things in the code... We pulled a ground at the same time as the main power wire.
As for the neighbors, apparently one of them called the township and said I was violating setbacks, so they called the inspector who called me. That is NOT a call you want to get. I was quite sure I was fine, but had to race out there in a panic to double check. Set back is 50' and my closest point was 57'+ so I was quite fine. But I was pissed that a nosy busybody obviously came up there when I wasn't around and then tried to make trouble over nothing.
I'll try to get another update or two out tonight.
More concrete
I had one more bit of concrete to pour. There was an 8x24' deck that was over the garage and needed a slab poured on it as the final surface, at least for the time being. I asked the main concrete outfit about it, and they said it was less risky as it was not on grade, and was insulated, so they could make it happen. That was great...until they gave me a quote. For this little slab they wanted over $10/sf! Insane. Not having better options, I scheduled it for the first week of Nov (and risking it getting too cold to really do right). In the mean time I started looking. A guy at work has a FIL that is a semi retired concrete guy. He was pretty much put away for the winter, but was willing to do this as it was reasonably small. So I booked him and cancelled the other guys. And the end result was I got the slab done for ~$800 instead of $2k. And this guy knows what he is doing, so that was good too. Here is a pic of the forms and insulation, and the final slab. It has been covered since then as it got real cold a couple days after the pour. It will probably stay that way until spring. There is a continuous EPDM rubber roofing membrane underneath to waterproof it. It has been great since I got the membrane in. It was pretty bad before that as it is exposed to the predominant wind/storm direction. Between the concrete cap (with a good slope for drainage) and the EPDM membrane, and the insulation board, and the ice dam below that, it should hold out :) Eventually we will cap it with stone or tile of some sort. Probably slate.
Deck%u00252520Slab%u00252520%u002525282%u00252529%u00252520%u00252528Medium%u00252529.JPG
Deck%u00252520Slab%u00252520%u002525286%u00252529%u00252520%u00252528Medium%u00252529.JPG
Windows and doors aka "The Great Window Panic of 2013"
A bit of a story here...
So this was one in a lengthy series of mad scrambles. The windows arrived at the lumber yard in Early/Mid Oct. We weren't quite ready and they were fully willing to store them for a bit, so no big deal. The problem I ran into was that my helpers were having other conflicts in Late Oct, so my help pool dried up right when it got critical. Then the other problem was I heard that the windows were ridiculously heavy due to the size and the oak trim. Well no big deal - we have a construction lift rental! Well when my help started to disappear, I asked them to extend then rental period for a week. It was due back Nov 4 early. They said no - it was already rented out. Crap. Well I now the panic started. I needed help, so I asked my framer if any of his guys were looking for extra work. One guy was so I hired him for a weekend. OK that helped and I figured we would be able to get a real good start on it the weekend of Oct 25th. Then it got worse. A few days ahead he said he got access to his new apartment and needed to move that weekend. Then my wife's mother passed away. Not totally out of the blue as she has been on the downside of cancer for a while, but nobody was expecting it then. So that weekend was totally toast, and it made for another crunch - this HAD to get done the next weekend.
The stars aligned a bit and I got help plus my hired help all on board. We started on Thurs (Halloween) and got a lot of the smaller stuff done then with just 2 of us. That was a great start. Then Fri came as there were 3 of us, so the plan was to start on the big windows as they were indeed heavy. We got the first one on the lift and ready to put in when the hired guy says "wait a sec - this ain't right" And he was right - the window was almost a foot short of the width of the rough opening. So we get to measuring and figuring out what is going on and it turns out the units that came pre-mulled were way short of the ROs spec'd by the software. A call to the lumber yard told me that I was hosed, and that he never double checked the ROs. I should have requested the ROs so I could verify them all, but chalk this one up to inexperience. The only saving grace is that it was not the other direction. We were able to frame-in the openings to match and proceed (heights were fine, just widths were off), but it cost us a lot of time that day, and a lot of money as all the openings were already prepped and ready to go. This was one key point that rubbed me the wrong way with the lumber yard as he basically told me "tough noogies". If they don't double check these things or give you the info to do so yourself, why are you paying them a premium? That really frosted me, as they has a full set of plans that included the window specs and ROs. I was beginning to feel like a second class citizen to them, and I guess I was "not in the club" by not being a contractor. After yet another similar issue a few weeks after this, I am done with them. I'm guessing another lumberyard might be better, as I have worked with them before and been happy. These guys were the ones the framers wanted to work with, so I went along. Lesson to the wise, I guess...
But in the end we got it done and all 32 windows and doors got installed that weekend before the lift had to go back. Some were 3 stories up and the mulled units were so heavy that 2 men could not reasonably lift them, so the lift was critical. So after all that venting, here are a couple pics...
Windows%u00252520and%u00252520doors%u00252520%u002525283%u00252529%u00252520%u00252528Medium%u00.JPG
Windows%u00252520and%u00252520doors%u00252520%u002525284%u00252529%u00252520%u00252528Medium%u00.JPG
Windows%u00252520and%u00252520doors%u00252520%u002525285%u00252529%u00252520%u00252528Medium%u00.JPG
Windows%u00252520and%u00252520doors%u00252520%u002525286%u00252529%u00252520%u00252528Medium%u00.JPG
Windows%u00252520and%u00252520doors%u00252520%u002525287%u00252529%u00252520%u00252528Medium%u00.JPG
Windows%u00252520and%u00252520doors%u00252520%u002525288%u00252529%u00252520%u00252528Medium%u00.JPG
Windows%u00252520and%u00252520doors%u00252520%u002525289%u00252529%u00252520%u00252528Medium%u00.JPG
Garage%u00252520doors%u00252520in%u00252520house%u00252520%u002525282%u00252529%u00252520%u00252.JPG
Since this point, the last garage door has been put in, and we got a temp front door, so the house is now fully enclosed and we have been working on the interior framing and such. Hard to show interior framing in pics, and I don't have much, so I may just skip that for now.
So I think that brings me up to current, though I am very unhappy at how cold it is now. That is killing me...
-Dave
   / A(nother) Home in the (different) Woods #167
Looks great, I like the windows you installed. What will you be using to insulate the ceiling?
Dave
   / A(nother) Home in the (different) Woods #168
Your house looks great. Very unique style(atleast for my area). I have to say, I've never seen a basement floor poured after the interior basement walls were already in place. I imagine that took some extra steps up front to make sure it would work out. With all the other home building threads coming to an end lately, I'm glad you started posting again. I think I was having home building withdraws! Keep up the good work, I look foreword to seeing the rest come together.
   / A(nother) Home in the (different) Woods #169
There is no cut and dry wording that makes it easy but a service turns into a feeder after the first disconnect. I don't know which code cycle you are on but I was looking through 2011 for these references.
There is a flow diagram in 230.1 that may help.
230.70 disconnect
215.6 Feeders
250.32 (b) (1) Grounding and Bonding
Local ammendments aside, if the service was run to your house, and you tapped off of the load side of the meter, and there is no ethernet, phone, cable, or any other metal between buildings, you could have run 3-wire to the garage.
955, Thanks. I never found a good ref either. We're on 2008 still. I used 230.6 to argue my case. There is a nice illustration showing my exact situation called exhibit 230.14. But you are probably right that the disconnect and the over current protection are what makes the break point (the flow diagram you pointed out seems to make it the breakers that actually are the delimiting point). Still annoys the crap out of me. I don't WANT my ground running back through conduit 300+ feet. I want it properly grounded and bonded at the house. That is the best way to deal with it. I don't see anything that indicates running from the house is any different than running from the shop. There will be Ethernet running between the buildings too. I suppose if I had to I could figure out fiber for that, but that would probably be painful.
Oh well...
   / A(nother) Home in the (different) Woods #171
Oh well...
Trust me, running a seperate ground is MUCH MUCH better, especially when other conductors are running between the buildings. Most people think the ground rod is the ground....it's not. The only purpose for it, and it sucks at that too, is to provide lightning and POCO accidential high voltage protection. The ground (earth) is a horrible conductor in most cases. Without the seperate ground (4th wire) the NEUTRAL is your ground conductor which carries 120 volt current and has voltage drop which gives you different ground potentials between the buildings. That is why the panel in your home should not have the neutral and ground bonded together.
Well I don't quite get it, other than the fact that you can have (and probably will have) different ground potentials at the 2 buildings. I tend to ground the heck out of my systems. I have 4x 10' ground rods at the main panel and 3 at the house plus it is grounded to the rebar in the concrete (inspector required that for some reason).
   / A(nother) Home in the (different) Woods #173
It's really looking great! Thanks for catching us up!
Wow it has been a long time since I updated.... 9-10 months! Sheesh OK, time to bring this up to speed. It has been a crazy year.
From where I left off, I like to call it 'the Winter Of Our Discontent". This was by far the worst winter i have seen in my 22 yrs here, and also the worst I have seen in my life. We spent most of the winter working on interior stuff, of course. Largely interior framing and mechanicals. I installed a natural gas fired heater around last thaksgiving to heat the place, and it did OK, but it was thirsty. We called it the Dragon. Gas bills were close to $500/mo for the 3 main winter months, and that hurt. This was insane cold for even here. Here it is. More to come...
   / A(nother) Home in the (different) Woods #175
Is your attic insulated? I'm sure glad I live where it rarely gets below freezing, and when it does happen, it's just for a few hours in the morning.
Eddie
Given how far behind I am, you need to keep in mind while reading this, that it was last winter - 2013-2014...
For those of you in the upper Midwest, you know how bad this winter has been, but frankly it is off-the-charts-insane. This has been, by far, the worst winter I have ever seen - in Western NY growing up, or here, in the 22 yrs I have lived here. We have had more below zero days than anytime since the 1800's, and who knows how accurate those records really are? And then snow storm after storm dropped inches upon inches of fluffy, white Global Warming on us. And since we have had only about 3 days above freezing since Dec 1, it has all stuck around, all winter. Below zero in March is basically unheard of, but here we are. Unreal.
What better time to build a house?
When November started turning into crap weather my friend Brook convinced me to get a temporary construction heater set up. I got that set up the day before Thanksgiving, and it was already way colder than normal. Come Dec ~4, it turned nasty and has not let up all winter. This is pretty much unprecedented in anyone's lifetime that is living now. Every winter has ups and downs, so we always get some melting in there and some big snow, but apparently Mother Nature has it in for me. We started this project with a crappy spring and summer in 2013, and the winter of 2014 will go down in the record books. I really just can't win with the weather. So I soldier on.
I had been hoping to move into insulation before it got too cold this winter, but the delays over the summer were too much, all the work took too long, and the weather turned too bad, too early, so we could not get to spraying foam at that point. And since it has stayed ridiculously cold for so long, plus the weather making all my work harder, we have not been able to get there yet...until now. Foam is now scheduled for the end of March. But Spring is breaking out (I think) and we are getting there. It has now turned a bit of Spring and the weather is warming dramatically (and suddenly...but then going back to Jan-Feb temps a lot too...can't win). But still, this is a very welcome sign that I was not too confident would happen this year...
Enough about the crappy weather... The time from Thanksgiving until early March was taken up with utilities work, for the most part. We also spent some time in late Jan early Feb moving the tools and equipment from our current house into the new shop. That is pretty well setup now, but I do not have dust collecting set up yet. It will be a while until I can get that going. On some of the worst cold days, I spent time getting the shop set up rather than freezing my butt off in the house. I keep the construction heater set low when not there to save money, so it takes time to heat back up. Hardly worth it for a couple hours in the evening when it is -15F out.
So here is a look at the electrical and the HVAC duct work. A lot of time went into all that. I did all the electric and low voltage wiring, and a guy I know from work who used to be an HVAC tech did all the duct work and furnace install. I can say for sure I underestimated how much time the duct work would take. Were I to do that myself, I would not yet be up to the point of being ready for insulation. It is good to have help.
A look at some of the early rough wiring in the house. Another thing you see here is plastic over all the doors and windows. Very early in the winter I was having huge frost issues on the woodwork of the windows and doors due to the stupid-cold temps so we had to cover them up to fix that. It did work, and has some other benefits like protecting the windows from dirt and minor damage. Plus we have to cover the walls with poly for vapor barrier at some point, so we did as much of that as we could at the same time.
Rough%u00252520wiring%u00252520-%u00252520early%u00252520%u002525281%u00252529%u00252520%u002525.JPG
Before the big wiring push you can see the main switch box array in the hallway.
Rough%u00252520wiring%u00252520-%u00252520early%u00252520%u002525282%u00252529%u00252520%u002525.JPG
Starting to get wires pulled in place. Lots of labeling to keep it all straight...
Wiring%u00252520main%u00252520switches%u00252520in%u00252520Great%u00252520room%u00252520%u00252.JPG
A look at the wires in the basement.
Rough%u00252520wiring%u00252520basement%u00252520%u002525281%u00252529%u00252520%u00252528Medium.JPG
And a look at the panel once it was fully finished. I figure it is good to have someone look at it since the dingbat inspector never even took the smallest peek at it. What kind of an electrical inspection doesn't even look at the main panel? All he cared about was if I had an outlet within 6' of any corner or door. Never looked at the main panel or any wiring methods. This inspires confidence. ...NOT! And of course this is one of the main reasons I won't let anyone else wire my house. I know I will do it right, even if the inspector doesn't check anything...
The big hallway switch array...before...
And after....
And "after" by the screen porch...
... And by the kitchen deck
More to come...
Here is some detail on the HVAC work (Heating Ventilation Air Conditioning). Primary heating is through radiant water tubing in the floors. This got complicated in several places. We also put in a full forced-air furnace mainly for the AC, but it is also nice to use as heat at times. Radiant is great for the winter, but it is slow response, as you have to heat a slab of concrete for example, before you really get heat out of it. If the days or nights are just a little cool, as typically happens in the spring and fall, you might not want to run the radiant for just one or two nights but need a little heat. A forced air furnace is great for this.
I will say upfront that I greatly underestimated the required time for ductwork. I lucked out though in that I work with a guy who used to be an HVAC tech around the cities. He has done the whole thing for me, and it has come out much better than it probably would have from a commercial outfit as we could discuss items as they came up, and at probably less than half the cost. It took him a lot of time, but I had too much else to do in the same time and there is no way I could have done this too. Plus not knowing some of the key details in how this is done would have hurt a lot. He has a couple details he is finishing up this weekend (4/12/14) and we will wrap up final inspection on that early next week. Then we move onto full drywall work. All other inspections are complete for now (rough electric, rough plumbing, insulation, framing).
Here is the temp gas manifold feeding "The Dragon"
Temporary%u00252520heat%u00252520%u002525284%u00252529%u00252520%u00252528Medium%u00252529.JPG
You can see some of the main ductwork runs here, including after insulation. Lots o' ducts. They foamed under all floors as it fills in easy and helps keep the radiant heat going where it should.
Start%u00252520duct%u00252520work%u00252520%u002525281%u00252529%u00252520%u00252528Medium%u0025.JPG
Start%u00252520duct%u00252520work%u00252520%u002525282%u00252529%u00252520%u00252528Medium%u0025.JPG
We did a lot of foam insulation to seal things up well. Here is a shot of the foam in the attics where they sprayed 2" of closed cell foam on the ceilings to seal everything up nicely. They did a very nice job of this. I was very impressed with the insulators overall- very good and professional. This was a very tight space to work in so it was all the more impressive what they did.
Foam%u00252520seal%u00252520ceilings%u00252520%u002525281%u00252529%u00252520%u00252528Medium%u0.jpg
Foam%u00252520seal%u00252520ceilings%u00252520%u002525283%u00252529%u00252520%u00252528Medium%u0.jpg
Let's talk radiant... The primary heat will be radiant heat. In the basement we buried the tubing in the slab. The main floor will be covered in detail below. The upper floor was done with a technique called staple-up. You basically staple the tubing to the bottom of the floor from below. You use thin aluminum plates to help distribute the heat and hold the tubing up. This is a hard way to do radiant but works OK for small areas, like the upper floor in this plan. This was a full weekend of work for two of us.
PEX%u00252520staple-up%u00252520bathroom%u00252520and%u00252520BR%u00252520%u002525282%u00252529.JPG
PEX%u00252520staple-up%u00252520library%u00252520%u002525281%u00252529%u00252520%u00252528Medium.JPG
PEX%u00252520staple-up%u00252520library%u00252520%u002525282%u00252529%u00252520%u00252528Medium.JPG
PEX%u00252520staple-up%u00252520library%u00252520%u002525283%u00252529%u00252520%u00252528Medium.JPG
Now for the main floor. This one is a bit different as we are doing it on top of the main floor deck. The techniques is to put the tubing down between 2x4 sleepers and the fill the space with concrete. then you put a subfloor of plywood/etc on top of that to ready the place for the finished floor. The house design was adjusted for this extra height. We had to wait on this as a lot of other things had to be in place first, but we have now knocked out the main level in just a couple weekends. Layout and the head scratching took some time, but once we figured out how we wanted to do it, it came together pretty quickly.
Main%u00252520floor%u00252520tubing%u00252520%u002525281%u00252529%u00252520%u00252528Medium%u00.JPG
Main%u00252520floor%u00252520tubing%u00252520%u002525282%u00252529%u00252520%u00252528Medium%u00.JPG
Main%u00252520floor%u00252520tubing%u00252520%u002525283%u00252529%u00252520%u00252528Medium%u00.JPG
Here is the progression of the great room. 1st step - layout and figuring it all out. Nothing nailed down yet.
Tubing%u00252520Great%u00252520Room%u00252520%u002525281%u00252529%u00252520%u00252528Medium%u00.jpg
Starting to layout tubing.
Tubing%u00252520Great%u00252520Room%u00252520%u002525282%u00252529%u00252520%u00252528Medium%u00.jpg
A couple pictures of the completed great room. I still need to do the intermediate sleepers in between the main ones shown, but that will happen this weekend. Then we will be ready to pour concrete there some time soon - in the next couple days.
Tubing%u00252520Great%u00252520Room%u00252520%u002525283%u00252529%u00252520%u00252528Medium%u00.jpg
Tubing%u00252520Great%u00252520Room%u00252520%u002525284%u00252529%u00252520%u00252528Medium%u00.jpg
Part of getting insulation done was wrapping up drywall on those ceiling areas that needed to be insulated, so I'll show that next as that is all done. The main drywall work will be starting in early May as I have hired a guy for that. I have too many other things to do, so that one needed to get hired out. I had planned to do more of the drywall but there just isn't enough time.
Insulation
I talked a bit about insulation in the last post. This was a great milestone to hit as it now means the house can be somewhat livable to work in. Only too bad it didn't happen in November before it was 150 below zero for 3 months!
The ceilings in the house are divided into two types: the cathedral great room and the truss framed roofs in the other sections (Master suite wing and upper level). These are handled differently for insulation. The great room gets 4" of closed cell foam sprayed directly on the underside of the roof deck, and then the remaining 10" of space are filled with dense pack cellulose giving the roof assembly something on the order of R-60. It is important to seal a cathedral ceiling like this with spray foam to avoid moisture/condensation problems in the future. This is the reason for spraying the closed cell foam first. The dense pack is to gain extra insulation at lower cost. If you want the building science details behind it, drop me a line. Otherwise everyone's eyes are probably glazed over by now as it is...
Here are some shots of the great room insulation in process. The first shot you can see the one side of the Big Beam is done with foam, and the other side was started. This was the end of day 1 which included a lot of prep and setup time.
great%u00252520room%u00252520ceiling%u00252520insulation%u00252520%u002525283%u00252529%u0025252.JPG
Here both sides are done foaming and they have put up netting on the first side that was already done with foam. This netting is air permeable so when they blow the cellulose in, the air that is used to blow it can come out through the netting to allow the cellulose to settle fully in.
great%u00252520room%u00252520ceiling%u00252520insulation%u00252520%u002525284%u00252529%u0025252.JPG
Here you can see the netting is all complete, and they have finished blowing in cellulose. The holes near the ridge beams are where they stuck the hose in to fill it up. If there was an obstruction, they poked in another hole to finish it off. I placed speaker boxes in the ceilings for future speakers for a general sound system or possibly for surround sound in the TV area. I just made these boxes out of some sheet foam.
great%u00252520room%u00252520ceiling%u00252520insulation%u00252520%u002525288%u00252529%u0025252.JPG
great%u00252520room%u00252520ceiling%u00252520insulation%u00252520%u002525289%u00252529%u0025252.JPG
They also foamed in under all floors to help the radiant heat go the direction it is supposed to (up). One thing that also had to happen was the duct work that was in the garage space needed to be foamed in with closed cell first to seal it in. This is the first picture. Note the ducts covered in foam above the red steel beam.
foaming%u00252520ductwork%u00252520in%u00252520garage%u00252520%u002525282%u00252529%u00252520%u.JPG
Then since the tuck under garage is considered unconditioned space, they foamed in 10" of the open cell foam for an R50 floor in the great room (directly over the garage). The open cell is really wild to watch them place it as it expands an incredible amount - a lot more than the closed cell. In the first pic you can see the main trunk duct below the trusses at the very bottom of the pic that was already sealed with closed cell. That was later enclosed in a soffit.
Ceiling%u00252520foam%u00252520lower%u00252520level%u00252520%u002525285%u00252529%u00252520%u00.JPG
Ceiling%u00252520foam%u00252520lower%u00252520level%u00252520%u002525286%u00252529%u00252520%u00.JPG
There was a whole lotta foam going on for a few days...
As for the Truss ceilings, the original plan was to just blow in cellulose. After talking with the insulation guys, and thinking it over, it made a lot of sense to first put down a seal coat of closed cell foam first on top of the ceiling drywall so everything would be totally air tight. No sense making the rest of the house perfect and leaving this without a good seal. So they did that first. But there was a wrinkle. I had been putting up plastic vapor barrier on the upper floor while they were working elsewhere in the house. Once I got that done was when we discussed foaming it first. And the guy told me the plastic was not very compatible with the foam so it was better to leave it out. So after nicely covering the entire ceiling, I tore it all out. I love tearing work out - NOT! But it will be better in the long run and only wasted $50 of poly, so such is life... Here it was before I tore it down. Figured it was worth a pic at least...
2nd%u00252520Floor%u00252520vapor%u00252520Barrier%u00252520%u00252528Large%u00252529.jpg
More radiant tubing next
   / A(nother) Home in the (different) Woods #179
Interesting. Any reason you sprayed the "attic floor" rather than the underside of the roof? We are looking at foaming the attic in the future but I had only looked at foaming the underside of the roof deck (vs foaming the "floor" of the attic).
Thanks
Aaron Z
   / A(nother) Home in the (different) Woods #180
Nice looking ceiling. Can you share some more info about your rafters? I've only seen them used on floors and didn't know you could use them on a pitch. I've been planning on using 2x12 for my addition, but those sure look a lot lighter and easier to handle. What do they cost?
Thanks,
Eddie
2018 Nissan Rogue SUV (A59231)
2018 Nissan Rogue...
2016 Freightliner M2 106 Ambulance (A59230)
2016 Freightliner...
FORD 545D TRACTOR (A60430)
FORD 545D TRACTOR...
2007 John Deere 644J Articulated Wheel Loader (A59228)
2007 John Deere...
2012 MACK Tender Truck w/ADAMS Rear Discharge Bed Auger (A56438)
2012 MACK Tender...
*Selling at Royal Auction Tampa, FL Location* (A59231)
*Selling at Royal...