Post frame vs foundation

   / Post frame vs foundation #11  
There is a lot of inherent shear strength in a pole-barn construction with the ends of the posts in the ground 3-4 feet, and diagonal braces between poles. With a framed wall, the shear strength will have to come from sheathing. There would be some shear strength from metal siding, but much more limited and probably more failure prone in certain scenarios, so I'd want OSB if it were my building. I doubt siding alone would pass code, which is some guidance to go by whether or not you need to get approvals/inspections.

When my dad had a construction business after he got out of homebuilding, he did a lot of contract jobs building guard shacks and portable buildings for gov agencies and military bases. For those, we'd use OSB over a 2x4 or 2x6 framed wall, and then screw steel siding over the top of the OSB (I do remember a lot of customers wanted steel siding with wood-grain texture and graphics, which always struck me as funny). The siding would usually get tacked on temporarily with an air stapler using 1/4" staples to hold in place, and then someone would come around behind that and drive 1" metal screws through the siding into the OSB. Don't remember the screw spacing, but it was on the order of 16-24" or so. It was a very strong combination and pretty much lifetime construction. The buildings would be subjected to a lot of moving loads from cranes, forklifts, construction equipment, etc, and were solid as heck. So that's one data point in favor of steel siding over OSB.

My current garage and last garage were framed walls directly on top of a block foundation, and I see no reason you couldn't use that for a shop/barn construction. Put j-anchors in the top of the wall to secure the sill (pressure treated) and bottom wall plate and you're good to go. There is a lot of new structural hardware that can help anchor the walls for the best results -- for instance angle plates that tie into the j-anchors and then run up a wall stud 12" and fasten with 8-10 1/4" structural screws. If the masonry work isn't an issue in terms of labor/cost, I think wall framing over block is a great way to go.

I can see how a few rows of block would be better for hosing out the place, but that's not something I'd want to do, since it introduces a lot of moisture into your work area that will take a while to go away. In the meantime it's all around your tools, materials, equipment, etc. I hosed out my workshop once, and never again.

There would certainly be a fire benefit to having some block on the wall, but unless it goes up pretty high, I'd say it will be marginal. There is so much other stuff that could still catch on fire. I'd probably do 1-2 courses of block above floor level, and then start the framed walls. Put up some scrap metal, hardi panel, drywall, etc in an area that might see a lot of sparks from welding/cutting/etc.

I don't think there is a real benefit to putting posts on top of a block wall -- you'd still need a ton of bracing and/or sheathing to get any shear strength, and I can't think of reliable ways to attach posts to block walls (reinforced solid concrete walls, yes, but not block walls).
 
   / Post frame vs foundation
  • Thread Starter
#12  
There is a lot of inherent shear strength in a pole-barn construction with the ends of the posts in the ground 3-4 feet, and diagonal braces between poles. With a framed wall, the shear strength will have to come from sheathing. There would be some shear strength from metal siding, but much more limited and probably more failure prone in certain scenarios, so I'd want OSB if it were my building. I doubt siding alone would pass code, which is some guidance to go by whether or not you need to get approvals/inspections.

When my dad had a construction business after he got out of homebuilding, he did a lot of contract jobs building guard shacks and portable buildings for gov agencies and military bases. For those, we'd use OSB over a 2x4 or 2x6 framed wall, and then screw steel siding over the top of the OSB (I do remember a lot of customers wanted steel siding with wood-grain texture and graphics, which always struck me as funny). The siding would usually get tacked on temporarily with an air stapler using 1/4" staples to hold in place, and then someone would come around behind that and drive 1" metal screws through the siding into the OSB. Don't remember the screw spacing, but it was on the order of 16-24" or so. It was a very strong combination and pretty much lifetime construction. The buildings would be subjected to a lot of moving loads from cranes, forklifts, construction equipment, etc, and were solid as heck. So that's one data point in favor of steel siding over OSB.

My current garage and last garage were framed walls directly on top of a block foundation, and I see no reason you couldn't use that for a shop/barn construction. Put j-anchors in the top of the wall to secure the sill (pressure treated) and bottom wall plate and you're good to go. There is a lot of new structural hardware that can help anchor the walls for the best results -- for instance angle plates that tie into the j-anchors and then run up a wall stud 12" and fasten with 8-10 1/4" structural screws. If the masonry work isn't an issue in terms of labor/cost, I think wall framing over block is a great way to go.

I can see how a few rows of block would be better for hosing out the place, but that's not something I'd want to do, since it introduces a lot of moisture into your work area that will take a while to go away. In the meantime it's all around your tools, materials, equipment, etc. I hosed out my workshop once, and never again.

There would certainly be a fire benefit to having some block on the wall, but unless it goes up pretty high, I'd say it will be marginal. There is so much other stuff that could still catch on fire. I'd probably do 1-2 courses of block above floor level, and then start the framed walls. Put up some scrap metal, hardi panel, drywall, etc in an area that might see a lot of sparks from welding/cutting/etc.

I don't think there is a real benefit to putting posts on top of a block wall -- you'd still need a ton of bracing and/or sheathing to get any shear strength, and I can't think of reliable ways to attach posts to block walls (reinforced solid concrete walls, yes, but not block walls).

Thanks for the reply.

My thought about putting posts on top of the block wall was all cost related. And would it be cheaper to do so, and space the trusses back to 8' or 12' OC and still have an acceptable level of strength. But further analyzing it, a simple stud wall on 24" centers with 4 OC trusses seems to be the cheapest.

As to the added cost of the foundation, that will be minimal. Have a backhoe, and block experience. So spending 1200 on block and mortar vs 1200 on 6x6 posts is a wash. Its my labor either way as nothing will need hired out. Which is where I think the majority of the cost difference comes from when reading online about how much more $$$ stick built is.

Hosing out is a non issue. Did it in my old garage that was OSB. But had to keep it away from the walls. With a wood burner and heated shop with a central floor drain, it dries quickly. Just dont want to have to worry when nearing the edges and getting them wet. As to fire and sparks, I think 2 row of exposed block will work. The cutting and welding is always done several feet away from a wall, as wall space is always tied up with tool boxes, shelving, air compressor, parts washer, etc. Just worried about the ones that roll across the floor and come to a rest at the walls edge.

I have been doing a ton more reading online, and 99% of what I read claims the 2 biggest benefits of post-frame is strength, and cheaper.

Well, cost is figuring the same with me doing the labor either way. So it really comes down to strength. The touted claim of having several posts 4' in the ground keepig it from blowing away.....with proper fastening of the wall to the block, I think it will be just as strong. And likewise, proper fastening of the roof structure to the wall.

So, while a post frame "may" be a little stronger, with never testing the limits of a foundation in my area, a post frame may be overkill. And if we do happen to have a once in a lifetime tornado roll through and destroy the garage, thats what I pay insurance for.

So for the time being, Here is what I am planning:
2' wide 6" thick footer with rebar
6 course 8" block wall
treated 2x8 GC rated sill plate. Properly anchored to filled cores in the block. (need to check into how many/how far apart these need to be.
Then I will pour the concrete floor to have a nice place to work
Pre-built wall sections with 2x6's stood up and anchored to the foundation
7/16 OSB sheathing all the way around
4' OC trusses w/2x4 purlins laid flat
Metal roofing and siding

Then will work on interior insulation, OSB walls, surface mounted wiring in conduit, lighting, etc

Now just waiting on the weather to break in a few months so I can dig a footer.
 
   / Post frame vs foundation #13  
Are screws into OSB adequate for holding siding? I'm pretty sure it's not for roofing, but maybe OK for siding. I like the idea of 2x4's mainly because you can use a good treated grade board, but maybe that doesn't matter much if your slab is well above grade.
 
   / Post frame vs foundation
  • Thread Starter
#14  
Are screws into OSB adequate for holding siding? I'm pretty sure it's not for roofing, but maybe OK for siding. I like the idea of 2x4's mainly because you can use a good treated grade board, but maybe that doesn't matter much if your slab is well above grade.

Not sure on the holding. I would think it would be sufficient. I have seen alot of houses go up with OSB sheathing for the roof with metal down on top.

Not sure 2x4's will give the lateral stiffness I need. Maybe with them + the steel??

No need to worry about a treated gradeboard. Site is flat, and will be 2 rows of block above ground topped with a treated board. The OSB wont come into contact with the ground or the block. And will extend the metal 6" or so down the block to eliminate the chance of rain blowing up under the metal siding and getting at the OSB
 
   / Post frame vs foundation #15  
Post frame buildings are very difficult to beat price wise and strength especially if you are going tall. That being said concrete in the ground is always better than wood in my book. You mentioned about doing your footing 6 inches thickI would recommend eight. And I know you said you have experience laying block but I am much more fond of poured walls. If you do decide to go stick framing in your walls I was curious why you were using two by sixes instead of two by fours? Is it because of height I didn't catch how tall you plan to build. On your truss spacing I preferred to go 2 foot on center and use half-inch OSB and then just use a standard shingled roof rather than steel and purlins. Some of the benefits that I like are that it minimizes condensation and is much quieter on uninsulated buildings. But if you're insulating won't make much of a difference either way.
 
   / Post frame vs foundation
  • Thread Starter
#16  
Post frame buildings are very difficult to beat price wise and strength especially if you are going tall. That being said concrete in the ground is always better than wood in my book. You mentioned about doing your footing 6 inches thickI would recommend eight. And I know you said you have experience laying block but I am much more fond of poured walls. If you do decide to go stick framing in your walls I was curious why you were using two by sixes instead of two by fours? Is it because of height I didn't catch how tall you plan to build. On your truss spacing I preferred to go 2 foot on center and use half-inch OSB and then just use a standard shingled roof rather than steel and purlins. Some of the benefits that I like are that it minimizes condensation and is much quieter on uninsulated buildings. But if you're insulating won't make much of a difference either way.

Good questions.

I like poured walls too, but the added cost of forming and material make it hard to justify for just a single story garage.

6"x 24 is what I am shooting for and will likely be thicker in areas. 6" will be the minimum. And 2' because I have a 2' bucket on the hoe. Dads 2-story with full block wall basement called for 8" x 24, So I think 6 should be sufficient. But will certainly research footer specs before committing.

2x6 walls is for strenght AND insulation. I want a well insulated shop, Especially with going 12-14' high ceilings.

4' OC trusses is strictly a cost thing. They are $126 per truss and require 19. 2' OC trusses are only $20 less and need 37 of them. So it makes it a few grand more expensive. And my preference is metal roof. I dont like shingles. So given metal roof, and no drywall underneath, I really dont see the need to go 2' trusses.

I am actually considering laying more block. Going 4' above ground that way I can use 8' lumber for the walls instead of 12'. 8' lumber is cheaper per ft than 12' lumber. Will just have to look at how much more laying a few more courses of block will be. And also have to consider how it will look from the exterior, and less insulating value for the bottom 4' of wall......decisions decisions..
 
   / Post frame vs foundation #17  
Yes the uninsulated block will be a heat sink. I no longer use 2x6 walls just for insulation. Instead I use 2x4 and use premium cellulose blown in. It gives me effective r17 and almost no air filtration and only costs about 10 percent more installed than if I install r 13 batts myself. Plus I save the difference between the 2x4 & 2x6. Don't forget you will need at least 2 runs of #4 re-bar in those footings. I use 3 in 24 wide. Remember the last place you want to skimp it's on the foundation it will be the hardest to repair if you have a problem. Sounds like it's going to be a very nice building whichever way you go.
 
   / Post frame vs foundation #18  
If your sheeting the interior walls with OSB why not just strap the out side with 1x4 to attach the metal to they'll hold roofing bolts much better than OSB . Your interior shting. will give you all the necessary strength combined with the exterior metal.
 
   / Post frame vs foundation
  • Thread Starter
#19  
If your sheeting the interior walls with OSB why not just strap the out side with 1x4 to attach the metal to they'll hold roofing bolts much better than OSB . Your interior shting. will give you all the necessary strength combined with the exterior metal.

good thought, but I wasnt planning on sheathing ALL of the inside.

The building will be 40x72. I will build a wall 40' deep into the building and have a 40x40 section that is insulated and heated. The back 32' is gonna be unfinished for now. Just tractor and equipment storage
 
   / Post frame vs foundation #20  
So for the time being, Here is what I am planning:
2' wide 6" thick footer with rebar
6 course 8" block wall
treated 2x8 GC rated sill plate. Properly anchored to filled cores in the block. (need to check into how many/how far apart these need to be.
Then I will pour the concrete floor to have a nice place to work
Pre-built wall sections with 2x6's stood up and anchored to the foundation
7/16 OSB sheathing all the way around
4' OC trusses w/2x4 purlins laid flat
Metal roofing and siding

Then will work on interior insulation, OSB walls, surface mounted wiring in conduit, lighting, etc

Now just waiting on the weather to break in a few months so I can dig a footer.


Sounds like a good plan to me, especially if you are comfortable laying block -- that is a big advantage being able to do your own masonry. As much as I appreciate the simplicity and fast progress of pole barn construction, and despite having used it on my barn, having a full on block foundation is preferable to me. If I had to do it again, I would have made my stick-on-block workshop bigger and detached from our home, and not built a separate pole barn.
 

Tractor & Equipment Auctions

2016 Big Tex 14LX 14ft 7 Ton T/A Dump Trailer (A50322)
2016 Big Tex 14LX...
2001 Acura MDX SUV (A53424)
2001 Acura MDX SUV...
2016 Godwin CD150M 6in Dri-Prime Pump S/A Trailer (A51691)
2016 Godwin CD150M...
2020 KUBOTA RTV X1100C UTV (A51406)
2020 KUBOTA RTV...
2010 Ford Edge SE SUV (A51694)
2010 Ford Edge SE...
2019 Fontaine EQ1 Hydraulic Equalizing Spreader (A52377)
2019 Fontaine EQ1...
 
Top