Adding 220v welding circuit to the shop/garage

   / Adding 220v welding circuit to the shop/garage #21  
Experience has shown that when the mineral spirits ignite, the paint brush handles will become charred....:cool:
 
   / Adding 220v welding circuit to the shop/garage #22  
Here is a photo of the main panel and the shop breakers.
I do remember the wire to the subpanel being copper.

After seeing your picture you have 100 amps feeding the sub panel and would be sufficient to handle the wielder along with the existing circuit. the handle tie on the red Bryant breaker would no longer meet a code requirement. :)
 
   / Adding 220v welding circuit to the shop/garage #23  
After seeing your picture you have 100 amps feeding the sub panel and would be sufficient to handle the wielder along with the existing circuit. the handle tie on the red Bryant breaker would no longer meet a code requirement. :)

Avoid doing any welding for an electrical inspector or your fire insurance agent.:)
 
   / Adding 220v welding circuit to the shop/garage #24  
I figured everything would be covered here but I notice there wasn't much discussion on the size of the welder circuit. Most home use welders are going with something like a 180 amp MIG these days, which seems to do almost anything you need. You can run these pretty hard on a 30 amp circuit, which is an economical installation. You will probably need to use a 50 amp plug/outlet, but don't let that confuse you. You can wire that up with no. 10 wiring as long as you have 30 amp breakers.

Lincoln, in particular, is very confusing on what service is required for their welders, but I have a Lincoln 180 on a 30 amp circuit and it has never been a problem. I found a Ebay seller with a real deal on 10/3 SOOW cable (braided, thick flexible insulation) and made a 60 ft. extension cord and life is now good.
 
   / Adding 220v welding circuit to the shop/garage #25  
I figured everything would be covered here but I notice there wasn't much discussion on the size of the welder circuit. Most home use welders are going with something like a 180 amp MIG these days, which seems to do almost anything you need. You can run these pretty hard on a 30 amp circuit, which is an economical installation. You will probably need to use a 50 amp plug/outlet, but don't let that confuse you. You can wire that up with no. 10 wiring as long as you have 30 amp breakers.

Lincoln, in particular, is very confusing on what service is required for their welders, but I have a Lincoln 180 on a 30 amp circuit and it has never been a problem. I found a Ebay seller with a real deal on 10/3 SOOW cable (braided, thick flexible insulation) and made a 60 ft. extension cord and life is now good.

with a little searching you will even find that it is generally safe and legal (i can't quote on specific laws everywhere) to run a 50a breaker and receptacle with wire smaller than 6/2 for a welder. this can be allowable based on the duty cycle of the welder. it's an area that causes heartburn with many people (especially on forums) but it isn't wrong. it does, however require special circuit labeling for the intended use/duty cycle appliance. this same thing is often done in hvac and cases where there are electric motors with high startup draws, but low continuous draws.

while it is acceptable, i would only use this setup in a situation where smaller wiring was already run and would be very difficult to change, such as through finished walls, or under under concrete/asphalt. if you are running a new circuit, i'd opt for matching the wire/breaker/receptacle sizes. generally speaking, a 50a breaker and receptacle with 6/2 copper will power most any device a homeowner is likely to have. when i did my garage i opted for 6/3 copper and just wire nutted and taped over the neutrals in the boxes. i figured that since i was sheathing over the inside walls, i would do this on the odd chance that some future appliance i bought might require a 120/240 circuit. easier than tearing it all up to rewire later.
 
   / Adding 220v welding circuit to the shop/garage #26  
I figured everything would be covered here but I notice there wasn't much discussion on the size of the welder circuit. Most home use welders are going with something like a 180 amp MIG these days, which seems to do almost anything you need. You can run these pretty hard on a 30 amp circuit, which is an economical installation. You will probably need to use a 50 amp plug/outlet, but don't let that confuse you. You can wire that up with no. 10 wiring as long as you have 30 amp breakers.

Lincoln, in particular, is very confusing on what service is required for their welders, but I have a Lincoln 180 on a 30 amp circuit and it has never been a problem. I found a Ebay seller with a real deal on 10/3 SOOW cable (braided, thick flexible insulation) and made a 60 ft. extension cord and life is now good.

NOPE: you SHOULD NOT wire a 50 amp outlet with #10 for a 30 amp circuit. This gives a future potential problem in that someone else down the line can assume that this 50 amp outlet is set up for a 50 amp circuit, and this causes problems. if you use a 50 amp receptacle, please wire it for 50 amps. better to have more power available than you need.

The NEC does not allow you to do this. it may work, but isnt right.
 
   / Adding 220v welding circuit to the shop/garage #27  
NOPE: you SHOULD NOT wire a 50 amp outlet with #10 for a 30 amp circuit. This gives a future potential problem in that someone else down the line can assume that this 50 amp outlet is set up for a 50 amp circuit, and this causes problems. if you use a 50 amp receptacle, please wire it for 50 amps. better to have more power available than you need.

The NEC does not allow you to do this. it may work, but isnt right.

i'm thinking that as long as the breaker and wire size match, an overrated receptacle is not an issue? if you plug a larger than allowable device in, it will only trip the breaker. i can't quote the code, but i can't see where there is any safety issue. i would think it would fall into the same category as my above post where i mentioned mismatched breaker/wire sizing. i came across that two (maybe three) years ago when i wired my garage for a welder. maybe something has changed? i agree that these situations are not ideal, but from what i read they are legal, acceptable, and safe, as long as they are done properly.

edit: as i said, i'm not a pro, but i did a lot of research before i did my shop. search for nec article 630 and read up if interested. i figured i'd add this to curb any rule of thumb debates that spawn due to my posts that do not necessarily support, but at the very least add legitimacy to this procedure.
 
Last edited:
   / Adding 220v welding circuit to the shop/garage #28  
i'm thinking that as long as the breaker and wire size match, an overrated receptacle is not an issue? if you plug a larger than allowable device in, it will only trip the breaker. i can't quote the code, but i can't see where there is any safety issue. i would think it would fall into the same category as my above post where i mentioned mismatched breaker/wire sizing. i came across that two (maybe three) years ago when i wired my garage for a welder. maybe something has changed? i agree that these situations are not ideal, but from what i read they are legal, acceptable, and safe, as long as they are done properly.

edit: as i said, i'm not a pro, but i did a lot of research before i did my shop. search for nec article 630 and read up if interested. i figured i'd add this to curb any rule of thumb debates that spawn due to my posts that do not necessarily support, but at the very least add legitimacy to this procedure.

This got me thinking...where in the code book is this listed. Its come up a few times over the years, and we have had to rate the cord, wires, breakers and plugs for the device.

I got out the code book (something i hate to do) and began perusing the 800+ pages. Heck if i can find it.

So i called one of my inspectors, and hes not even sure where its in the book, but he told me that to be legal, a welder needs a MOLDED case cord plug rated for the equipment. The wires feeding the plug AND the breaker have to be rated to match the receptacle. However, welding circuits can be rated up to 200% of listed capacity to allow for startup.

So a welder rated at 30 amps is usually fed from a 50 amp circuit. The cordset attached to the welder will be over-sized and IF it has a 50 amp plug and it HAS to be fed with a 50 amp circuit.

Hes going to see if he can find the actual code, but told me its Monday.....too early for him to look. he'll get back to me.


UPDATE:

Article 210.21(B)(3) Table

Receptacle Ratings for Various size circuits

the table is included here. He further tells me that some inspectors allow the 30 amp circuit using a 50 amp recepticle, but he doesnt allow it. so i guess its ok as long as your not cought.
 

Attachments

  • code book 210.21small.pdf
    348.8 KB · Views: 339
   / Adding 220v welding circuit to the shop/garage #29  
i'm thinking that as long as the breaker and wire size match, an overrated receptacle is not an issue?

I am not a pro either but I agree with this.

You see 20A 120v recepticles wired with 14ga and a 15 amp breaker all the time. Same difference here.

Oversizing the recepticle/plug is not a problem

Oversizing the wire is not a problem

Oversizing the breaker...BIG PROBLEM
 
   / Adding 220v welding circuit to the shop/garage #30  
I am not a pro either but I agree with this.

You see 20A 120v recepticles wired with 14ga and a 15 amp breaker all the time. Same difference here.

Oversizing the recepticle/plug is not a problem

Oversizing the wire is not a problem

Oversizing the breaker...BIG PROBLEM

The code does allow a 20 amp or a 15 amp receptacle wired to a 20 amp circuit in RESIDENTIAL situations only. in commercial it does not allow this.

As you can see in the above PDF chart. Its very specific in the 30 and 50 amp ratings.
Hay, i dont write these **** rules, i only have to follow them

I dont agree with them
 

Attachments

  • code book 210.21small.bmp
    173.7 KB · Views: 661
   / Adding 220v welding circuit to the shop/garage #31  
The code does allow a 20 amp or a 15 amp receptacle wired to a 20 amp circuit in RESIDENTIAL situations only. in commercial it does not allow this.

As you can see in the above PDF chart. Its very specific in the 30 and 50 amp ratings.
Hay, i dont write these **** rules, i only have to follow them

I dont agree with them

Kinda odd how they will allow a 15A recepticle on a 20A circuit.

That sounds more dangerous than a 20a recepticle on a 15a circuit:confused2:
 
   / Adding 220v welding circuit to the shop/garage #32  
Kinda odd how they will allow a 15A recepticle on a 20A circuit.

That sounds more dangerous than a 20a recepticle on a 15a circuit:confused2:

That it does....but its the great NEC cra* shoot i go thru every day..

Sometimes i wonder why i didnt become a plumber
 
   / Adding 220v welding circuit to the shop/garage #33  
The section on receptacles really surprises me. Does the exception referring to 630.11 allow a 50A receptacle on a lighter circuit? (I don't have a code book.) In my experience, it's a really common practice to put 50A receptacles on 30A circuits, pushed in part by welder manufacturers putting those 50A cords on machines that don't require it.

I don't know why they do it, but I don't think you could ever run my Lincoln 180 hard enough to pop a 30A breaker and most people could probably get by with a 20 amp.
 
   / Adding 220v welding circuit to the shop/garage #34  
Come on guys,, think about it for a min. If you have a 20a 120 volt circuit with a 15a outlet.. Well this outlet has 2 places to plug in not just one.. say you have 2 .. 8 amp loads you want to plug in,,,, each side of the outlet is rated for 15a.. If everything was wired and torqued properly it should run for a very long time with no problems..
 
   / Adding 220v welding circuit to the shop/garage #35  
Not replying to anyone in particular. The NEC does allow 15A or 20A receptacles on a 20A circuit, provided there are more than 2 or more receptacles on that circuit. No restriction commercial or residential. NEC 210.21(B)(3).

The welder outlet can be supplied with #10AWG wire and protected by a 50A breaker. Look at the Overcurrent Protection for conductors in NEC 630.12(B). The wires can be protected at not more than 200% of the conductor ampacity. Article 240.3 specifically points you to Article 630 for conductors supplying a welder. The ampacity charts in NEC 310 no longer apply.
Enforcing the NEC has been my life for the last 23 years. I've taken flak before for posting the above, but that's OK, I have my appropriate PPE on.......LOL
 
   / Adding 220v welding circuit to the shop/garage #36  
The section on receptacles really surprises me. Does the exception referring to 630.11 allow a 50A receptacle on a lighter circuit? (I don't have a code book.) In my experience, it's a really common practice to put 50A receptacles on 30A circuits, pushed in part by welder manufacturers putting those 50A cords on machines that don't require it.

I don't know why they do it, but I don't think you could ever run my Lincoln 180 hard enough to pop a 30A breaker and most people could probably get by with a 20 amp.

630.11 just rates the multiplication factor for ark welders based on their duty cycles. .. and this is more or less applicable to multiple welders.
 

Attachments

  • welder.pdf
    428.7 KB · Views: 212
  • welder.bmp
    492.8 KB · Views: 386
   / Adding 220v welding circuit to the shop/garage #37  
Not replying to anyone in particular. The NEC does allow 15A or 20A receptacles on a 20A circuit, provided there are more than 2 or more receptacles on that circuit. No restriction commercial or residential. NEC 210.21(B)(3).

The welder outlet can be supplied with #10AWG wire and protected by a 50A breaker. Look at the Overcurrent Protection for conductors in NEC 630.12(B). The wires can be protected at not more than 200% of the conductor ampacity. Article 240.3 specifically points you to Article 630 for conductors supplying a welder. The ampacity charts in NEC 310 no longer apply.
Enforcing the NEC has been my life for the last 23 years. I've taken flak before for posting the above, but that's OK, I have my appropriate PPE on.......LOL


yeiks.......#10 MAY be rated for 50 amps ?? where do yo find this little tid bit?

i guess ill have to go buy a 2011 code book. they have just come out at our supply house. Im not due to take classes in the 2011 changes for 3 months.

Ive lived by tables 310....for ever. are you telling me that they no longer are going to be used???

And what about the caveat that stated that #14 shall not exceed 15 amps, #12 not exceed 20 amps and #10 not exceed 30 amps...EVER, no matter what the temperature.


210.21 that i posted earlier stated the info about the 15 amp recepticle on a 20 amp circuit.


Personally, i wish they did away with the entire code book.
 
   / Adding 220v welding circuit to the shop/garage #38  
yeiks.......#10 MAY be rated for 50 amps ?? where do yo find this little tid bit?

as i've stated a few times, i'm not a professional, so my answer may not have the proper terminology, but the theory behind it should be correct. this isn't some new regulation, it's been there for some time. it is based solely on the circuit being used for a welder (duty cycle driven machine).

we all know that when a breaker sees a load in excess of its capacity, it trips instantly. when a wire sees an excessive load it does not instantly melt and burn the house down. it slowly heats up, and if the load is applied for too long, failure could then occur. since welders have a duty cycle - homeowner sized machines often have duty cycles of 20%-40%, meaning that in a given 10 minute period, the welder can only draw that maximum load for 2 to 4 minutes. because of this, the wire that is overstressed can cool down safely before the load is applied again. there is a calculation to determine how much you can undersize the wire by. i'm sure the previous poster can provide a link, and can probably explain it better than my layman's attempt.
 
   / Adding 220v welding circuit to the shop/garage #39  
Kinda odd how they will allow a 15A recepticle on a 20A circuit.

That sounds more dangerous than a 20a recepticle on a 15a circuit:confused2:

Well think about it this way - you plug in a lamp to that 15 or 20A outlet. The lamp has 18 ga cord (pretty common). 18 ga isn't rated for even close to 15A, much less 20A so how is that allowed? For single family residential outlets, the code allows you some leeway with 15 & 20 A outlets, mostly as a convenience, IMHO. It allows you more flexibility to wire outlets on a 20A circuit for less breaker tripping potential, without requiring the 20A plug. An actual 20a 120V plug is pretty rare, but I have seen them a couple times in my life.
 
   / Adding 220v welding circuit to the shop/garage #40  
Well think about it this way - you plug in a lamp to that 15 or 20A outlet. The lamp has 18 ga cord (pretty common). 18 ga isn't rated for even close to 15A, much less 20A so how is that allowed? For single family residential outlets, the code allows you some leeway with 15 & 20 A outlets, mostly as a convenience, IMHO. It allows you more flexibility to wire outlets on a 20A circuit for less breaker tripping potential, without requiring the 20A plug. An actual 20a 120V plug is pretty rare, but I have seen them a couple times in my life.

there not rare, just expensive. There called spec grade recepticles, and we use them on commercial jobs. There in the $6-8.00 range. But at least they dont have that crappy tamper resistance rating that i truly hate.

Anyone that allows those TR outlets to remain in their homes is a NUT IMHO....for what its worth. Stupid codes require all 110 outlets in residential to be tamper resistant, but NOT 220 outlets. 220 will KILL a kid, 110 will just shock them and make them think twice about doing it again.
 

Marketplace Items

2016 FORD TRANSIT T250 CARGO VAN (A59905)
2016 FORD TRANSIT...
2013 ISUZU NPR STAKE BODY TRUCK (A59904)
2013 ISUZU NPR...
2017 Ford Transit 350 Passenger Van (A59230)
2017 Ford Transit...
pressure washer, and trailer (A56859)
pressure washer...
2012 Mini Cooper Coupe (A59231)
2012 Mini Cooper...
2019 KUBOTA KX033-4 EXCAVATOR (A60429)
2019 KUBOTA...
 
Top