Electrical question.

   / Electrical question. #11  
If you have a sub panel in your barn/shop from the main panel in the house, check to see if the neutral and ground buss bars (in the sub panel) have a strap connecting them. If so, turn off the breaker to the sub panel in your main breaker box in the house, and disconnect the strap in the sub panel.

Might be a long shot, but if the barn/shop panel does not have its own meter, then these to buss bars shouldn't be connected.
 
   / Electrical question. #12  
If you have a sub panel in your barn/shop from the main panel in the house, check to see if the neutral and ground buss bars (in the sub panel) have a strap connecting them. If so, turn off the breaker to the sub panel in your main breaker box in the house, and disconnect the strap in the sub panel.

Might be a long shot, but if the barn/shop panel does not have its own meter, then these to buss bars shouldn't be connected.
Not so….in older homes, they only ran 3 wires between buildings and drove new ground rods at the secondary buildings. In these cases you leave the bonding jumper inplace. In more modern houses, they run 4 wires between buildings, and this is the case you dont want to bond ground and neutrals.
 
   / Electrical question.
  • Thread Starter
#13  
If you have a sub panel in your barn/shop from the main panel in the house, check to see if the neutral and ground buss bars (in the sub panel) have a strap connecting them. If so, turn off the breaker to the sub panel in your main breaker box in the house, and disconnect the strap in the sub panel.

Might be a long shot, but if the barn/shop panel does not have its own meter, then these to buss bars shouldn't be connected.
I think it does.

20230819_164218.jpg
 
   / Electrical question. #14  
If you have a sub panel in your barn/shop from the main panel in the house, check to see if the neutral and ground buss bars (in the sub panel) have a strap connecting them. If so, turn off the breaker to the sub panel in your main breaker box in the house, and disconnect the strap in the sub panel.

Might be a long shot, but if the barn/shop panel does not have its own meter, then these to buss bars shouldn't be connected.
If there are four conductors running to the barn/shop, then this would be good advise. Line 1, Line 2, Neutral, Grounding conductor.
 
   / Electrical question. #15  
If this is your sub panel in the barn/shop, I would turn the power off and remove that strap connecting the neutral and ground bar together.
Only place a connection like this should occur is at the main panel. All sub panels should isolate the the ground bar from the neutral bar.
 
   / Electrical question. #16  
I don't know much on the topic, but we had a whole house surge protector added when we did some other work. It really seemed to cut down on problems. In our case it was spike during thunderstorms that damaged electronics and even blew out a transformer plugged into an outlet. Completely fried the outlet, too.

Don't know if it would help OP. Listen to those guys that actually know about electricity. I leave that to the pros.
 
   / Electrical question. #18  
I have a box in the barn that is fed from the house. It is an aluminum wire.
Is your home’s internal wiring from breaker box to loads wired with aluminum conductors? Many homes built in the 1960s thru the mid 1970s have aluminum internal wiring.
 
   / Electrical question. #19  
If this is your sub panel in the barn/shop, I would turn the power off and remove that strap connecting the neutral and ground bar together.
Only place a connection like this should occur is at the main panel. All sub panels should isolate the the ground bar from the neutral bar.
Agree, you have a modern 4 wire fed subpanel. Lose the jumper bar. And that panel is a mess. if my employee did something like that, hed be unemployed that same day.

IMG_6470.jpeg
 

Attachments

  • IMG_6471.jpeg
    IMG_6471.jpeg
    588 KB · Views: 94
   / Electrical question. #20  
Neatness counts and can avoid problems is my take…
 

Tractor & Equipment Auctions

Light Tower (A52377)
Light Tower (A52377)
2007 Mack Granite CT713 Day Cab Truck Tractor (A53117)
2007 Mack Granite...
2004 Ditch Witch RT70M Ride On Trencher (A53117)
2004 Ditch Witch...
2012 Tiger 130BBL Vacuum Trailer (A53117)
2012 Tiger 130BBL...
2011 Ford Crown Victoria Sedan (A51694)
2011 Ford Crown...
22ft Rolloff Flatbed Body (A51691)
22ft Rolloff...
 
Top