Welder / Wiring for Small Garage

/ Welder / Wiring for Small Garage #41  
For small wire sizes it is easy to remember if you just add 10 amps starting with #12 being 20. Then #10 is 30 amps , #8 is 40 amps and #6 is 50 amps. Wire length and temperature rating will change the amperage. Just a rule of thumb for the lower temperature. A larger welder could be used on the 30 amp circuit but it would limit how high of setting you could use and the duty cycle.
 
/ Welder / Wiring for Small Garage #42  
JUst use receptacle that matched power cord on welder, don't cut off plug of welder cord and graft on something different, this is no brainer because receptacles is not a problem.... And the NEMA 6-50 plug/receptacle combination has become industry standard (in most cases) .... Now all you have to do is determine wire size and breaker amperage.....

As a side note if you are using a 120/240 volt machine manufacture's recommend not cutting off plug on welder cord and grafting on something different....Will probably also void warranty...
 
/ Welder / Wiring for Small Garage #43  
pulled a page from the owners manual 24 amps on 240 volt so that is 80% of a 30amp circuit breaker so you will need a 30 amp CB and #10 wire unless it is a really long run.
Copied and pasted this note from your attachment.

4-4. Unit Specifications For 230 VAC
Do not use information in unit specifications table to determine electrical service requirements. See Sections 5-8 and 5-12 for information on con-
necting input power.
 
Last edited:
/ Welder / Wiring for Small Garage #44  
JUst use receptacle that matched power cord on welder, don't cut off plug of welder cord and graft on something different, this is no brainer because receptacles is not a problem.... And the NEMA 6-50 plug/receptacle combination has become industry standard (in most cases) .... Now all you have to do is determine wire size and breaker amperage.....

As a side note if you are using a 120/240 volt machine manufacture's recommend not cutting off plug on welder cord and grafting on something different....Will probably also void warranty...
Most 120/240 machines include an adapter. Some machines cone with a 4 wire plug and I have one that is 3 phase also.
 
/ Welder / Wiring for Small Garage #45  
Copied and pasted this note from the your attachment.

4-4. Unit Specifications For 230 VAC
Do not use information in unit specifications table to determine electrical service requirements. See Sections 5-8 and 5-12 for information on con-
necting input power.
that is interesting, did not read that but then again we are not sizing a service we are sizing a feeder and the specified current draw is exactly what is used for that calculation.
 
/ Welder / Wiring for Small Garage #46  
You shouldn't use 8/3 for a 30 amp breaker, the coded size for 30 amp is # 10 wire, any size larger than that with a 30 amp breaker could cause a problem. It would take longer for a breaker to trip
Huh??? You can use any larger size wire, it's just a waste of money. If you are depending on losses in the wiring to trip the breaker, you have some serious problems.
 
/ Welder / Wiring for Small Garage #47  
#12 is 20 amp rated not 30.
I'm guessing that a #12 extension cable would be OK to use on a 30 amp welder because of the duty cycle. I think it would be frowned on for the building wiring because of the potential of hooking up a constant 30 amp load.
 
/ Welder / Wiring for Small Garage #48  
Huh??? You can use any larger size wire, it's just a waste of money. If you are depending on losses in the wiring to trip the breaker, you have some serious problems.
The only limitation on larger size wire is getting it to fit into the breaker or receptacle. Nothing to do with load.
 
/ Welder / Wiring for Small Garage #49  
All, question on wiring and breaker for my personal use small garage.

I have a 50 amp circuit from my house to the garage on 6/3 wire (black, red, white and ground).

I planned to wire a 30 amp circuit for welding with 8/3 wire, but is that enough for say a Hobart Handler 210MVP or a Mult-Handler 200 Multiprocess? I wouldn’t ever need to weld anything thicker than 3/8”.


Handler® 210 MVP™ MIG Welder | HobartWelders

Multi-Handler 200 Multiprocess Welder | HobartWelders

Will a 30 amp circuit with 8/3 work?
Electric works on demand .. so 6/3 run into a small panel and a 50 amp welder fed from that should be plenty for one person using one piece of equipment at a time. If you have a/c or compressor etc, switch them off if welding a long spell.
 
/ Welder / Wiring for Small Garage #50  
I'm guessing that a #12 extension cable would be OK to use on a 30 amp welder because of the duty cycle. I think it would be frowned on for the building wiring because of the potential of hooking up a constant 30 amp load.
cords are considered manufactures wiring and falls under different jurisdiction, usually UL.
 
/ Welder / Wiring for Small Garage #51  
When running 240vac the current load is shared by both hot legs so factor that into your wiring choice. For example if welder pulls 30 amps each leg supplies 15 amps so wiring can be determined by that and wire run length.
wire it and use welder for 240vac and forget about using it with 120vac IMO.
That is incorrect. Each leg carries the full 30 A.
 
/ Welder / Wiring for Small Garage #52  
The answer to your requirements is in the printed information under the voltage/amps chart. It states that the power cord is 240v 50 amps.
Good luck plugging that 50 amp cord into a 30 amp receptacle. If you replace it with a 30 amp plug—bye bye bye to your warranty.
The chart also shows in the last column 34 max amps.
I would do 1 central 50 amp plug centered on the non 30’ wall and build up 1 50 amp cord to be able to reach several feet out of the bay doors (50 feet?).
you can install a 50a outlet on any size wire you want, the circuit breaker needs to be 50a or less, the load has to be less than the wire size but nothing stopping you from installing upgraded components as long as they meet/exceed the requirements.
 
/ Welder / Wiring for Small Garage #53  
You shouldn't use 8/3 for a 30 amp breaker, the coded size for 30 amp is # 10 wire, any size larger than that with a 30 amp breaker could cause a problem. It would take longer for a breaker to trip
actually it would trip faster under a fault condition and be the same otherwise, as others have stated other than making it fit and cost considerations, no problem, in fact it is sometimes required to meet voltage drop requirements.
 
/ Welder / Wiring for Small Garage #54  
Why would the breaker take longer to trip with larger wire? I would think if anything it would trip faster as the larger wire would allow greater current under a short condition.
 
/ Welder / Wiring for Small Garage #56  
I did something similar but ran 2 ga for about 40 feet. I put in a 100 Amp sub-panel with the idea that I would rather have extra capacity in case plans change later on. I have an 80 gallon compressor and a Lincoln 255 mig machine on it. it is going to obviously cost more but I have flexibility for later on.
 
/ Welder / Wiring for Small Garage #57  
I'm guessing that a #12 extension cable would be OK to use on a 30 amp welder because of the duty cycle. I think it would be frowned on for the building wiring because of the potential of hooking up a constant 30 amp load.
Good post, The duty cycle hasn't been discussed much in this thread. Duty cycle is the reason that the manufacturer has written in the manual that #12 conductors rated for 75 degree C is the minimum size required for the installation.

From memory after reading in the manual the duty cycle for the Multi-Handler at 240 Volt AC and 170 DC output is approximately 20%. (looked it up, See section 4-11)
Duty cycle for welders is always based on a 10 minute time of use. So for the 20% duty cycle the welder would be off for 80% of the time, and on for 20% of the time. Hence the smaller conducter size allowed by the manufacturer.

Once again, Manufacturers written instructions supercede the NEC.

In the Manufacturers Manual for these welders there is a note (Section 5-9)that says,
5-9. Input Power Extension Cord Data
Use extension cord only for temporary wiring. Remove extension cord immediately after completing the project.

Cord Type Minimum Conductor Size Number of Conductors

Heavy Duty (Hard Usage) 12 AWG (4 mm2) 3

. Read OSHA Standard 1910.334 for more information on the use of cord and plug connected equipment. Read National Electrical Code (NEC) Article 590 for more information on temporary wiring.

Input 17 2018-11
Maximum Cord Length
50 ft (15 m)

Heavy Duty (Hard Usage) cord is rated for 600 Volts. So Cord type would need to be type SO cord or type ST cord.
 
Last edited:
/ Welder / Wiring for Small Garage #58  
I understand that the breaker protects the wiring of the circuit.

Where would I find chart that shows # 8 copper can handle 55 amps? I thought # 6 was only rated for 50 amps.
The attached has an ampacity table for conductors and gives us a flow chart to help comply with code, the flow chart is base on Electrical Theory. More going on here than there is room in this thread to explain. "Physics at work" is the best short explanation.
 

Attachments

  • NECAmpacityWorkflow.pdf
    165.8 KB · Views: 166
/ Welder / Wiring for Small Garage #59  
Duty cylce note from section 4-11 in manual.


Duty Cycle is percentage of 10 minutes that unit can weld at rated load without overheating.

If unit overheats, output stops. Wait fifteen minutes for unit to cool. Reduce amperage or duty cycle before starting to weld again.

NOTICE − Exceeding duty cycle can damage unit and void warranty.
 
/ Welder / Wiring for Small Garage #60  
#12 is 20 amp rated not 30.
True, except the code has to give allowance for Physics/Theory. One example would be motor loads. Breakers for motor loads need to be sized to allow for the inrush of current. So the NEC allows for breakers to be sized at approximatley 250% of motor running amps. As long as the conductor size has sufficient ampacity to serve the running amps load plus 125%, the breaker can be larger than the running amp by up to 2.5 times. (My paraphrase, Not code verbage cause I'm not taking the time to look it up.)

If you look at Art 630 of the NEC for overcurrent protection of welder conductors, the verbage is basically that conductors supplying welders shall be protected by an overcurrent device rated no more than 200% of the conductor ampacity.
So a 20 amp rated conductor could have a 40 amp breaker protecting it.
There is a formula for calculating this in 630.12.B



For inverter resistance welders. You would use Art 630.31.A, basically states that the conductor ampacity shall not be less than 70% of the rated primary current for seam welders and automatically fed welders that can be adjusted for different values of primary current and duty cycle. And not less than 50% of the rated primary current if there are other circumstances.
There are to many variables to go into here.

At least for the last 25 years of doing electrical drawings the minimum conductor sizes for welders was given in the operators manual for each welder. See attached sheets that have been previously posted showing this. I have never placed an approved stamp on a one line drawing without looking at the engineered data in a welders operators manual. The engineering calculations are placed in the operators manual, so I never bother with figuring it out. It has become thier liabilty.

I did at times have to have pictures of nameplate data sent, so I could size conductors and overcurrent protective devices.

From the welders manuals in this thread. One manual stated the minimum counductor size being a #14, the other manual stated the minimum conductor size as being #12. Both manuals stated that a "hard service cord" of #12 conductors were the minimum for an extension cord for up to 50 feet in length. The manuals also had the sizes for overcurrent protection provided.
 
Last edited:

Marketplace Items

2015 Freightliner M2 106 AWD Altec AT37G Bucket Truck (A60460)
2015 Freightliner...
DEUTZ MARATHON 60KW GENERATOR (A58214)
DEUTZ MARATHON...
2004 VE ENTERPRISES 500BBL FRAC TANK (A58214)
2004 VE...
2016 GENIE S65 TELESCOPIC BOOM LIFT (A60429)
2016 GENIE S65...
Preliminary Listing / Full Catalog Coming Soon! (A57148)
Preliminary...
2003 Big Tex 10PI 16ft. T/A Pipe Top Utility Trailer (A55973)
2003 Big Tex 10PI...
 
Top